    Rheem Heat Pump

    New Rheem heat pump been installed for a few months and customers states that hammering noise is periodically coming from air handler. In heat mode the pressures are 240 suction and 230 head. Suction temp is 114 and LL temp is 78. It was a 65 degree day today and in cooling mode the pressures were 135 head and 47 suction. There was frost starting to build up at the txv on condenser. Im thinking there are non condensibles in the system so purge system, replace txv and LL drier, weight in factory charge and see what that does. Any other suggestions?

  2. #2
    Join Date
    Mar 2019
    Posts
    22
    Post Likes
    It sounds low on charge . In the heating mode I’m guessing you just had your manifold hooked up in the standard cooling configuration. Low side hooked up to the suction line and the red hose hooked up to the liquid line . In heating you should hook the manifold with the blue hose to the true suction and your red hose to the discharge line which in cooling is your suction line .

  3. #3
    Join Date
    Dec 2012
    Location
    columbus, OH
    Posts
    6,952
    Post Likes
    Not sure about the hammering but it sounds low on charge to me...


    Sent from my iPhone using Tapatalk

  4. Likes jmeadows liked this post
  5. #4
    Join Date
    Jun 2017
    Location
    Portland, OR(Previous: Arizona, Texas, Oklahoma)
    Posts
    70
    Post Likes
    240 PSI for 410A is roughly 80 degrees Fahrenheit..

    Your suction temp is 113 degrees?

    Something ain't right

    I'm with the low on charge assumption

    Sent from my LM-G710VM using Tapatalk

  6. #5
    Join Date
    Sep 2007
    Location
    State College, PA
    Posts
    2,927
    Post Likes
    Quote Originally Posted by FreeThrowGuy View Post
    240 PSI for 410A is roughly 80 degrees Fahrenheit..

    Your suction temp is 113 degrees?

    Something ain't right

    I'm with the low on charge assumption

    Sent from my LM-G710VM using Tapatalk
    Numbers look like R-22.

    Wonder if just the outdoor was replaced.

    Matched system?
    Can someone please explain to me -
    Why is there never enough time to do it right the first time, but plenty of time to do it twice?


    Please view site rules: http://hvac-talk.com/vbb/showthread.php?t=1241

    Apply for Pro Membership: http://hvac-talk.com/vbb/showthread.php?t=116113

    Find your local HVAC-Talk Contractor: http://hvac-talk.com/aop

  7. #6
    Join Date
    Mar 2018
    Location
    Kansas Flatlands
    Posts
    388
    Post Likes
    Quote Originally Posted by joemach View Post
    Numbers look like R-22.

    Wonder if just the outdoor was replaced.

    Matched system?
    And it ain't cooling either

  8. #7
    Join Date
    Jan 2004
    Location
    PA
    Posts
    78,349
    Post Likes
    Quote Originally Posted by Mr. Nobody View Post
    New Rheem heat pump been installed for a few months and customers states that hammering noise is periodically coming from air handler. In heat mode the pressures are 240 suction and 230 head. Suction temp is 114 and LL temp is 78. It was a 65 degree day today and in cooling mode the pressures were 135 head and 47 suction. There was frost starting to build up at the txv on condenser. I’m thinking there are non condensibles in the system so purge system, replace txv and LL drier, weight in factory charge and see what that does. Any other suggestions?
    In heat mode, the large line is not a suction line. Its a high pressure hot gas line. You need to connect your manifold to the true suction port to read the suction pressure.

    If you connect your manifold to the true suction and liquid line, I think you'll see that it shows as a low charge in both heating and cooling mode.

    You can also recover and weigh how much charge was in the system. To see if its low on charge, or another problem.

    Would hate to have you replace the TXV and LLFD and then a few months or a year or two down the road, have the same problem because it was a leak problem.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  9. #8
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,082
    Post Likes
    I am wondering if both the indoor and outdoor units were replaced, and if someone actually had this working right from day one. Let us know what you find.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  10. #9
    Join Date
    Sep 2007
    Location
    edmonds wa
    Posts
    4,431
    Post Likes
    Model an serial numbers on all, plus a a little more diagnostic info is in order first.