    Midea or carrier

    Hi guys first time post we installed a midea 5ton mini split in April .system ran good until the weather got cold .now system is freezing at night when temperature drops.I notice condenser fan are running at full speed I thought they would slow down for low ambient control .suction pressure 98 sh 0 slt 30 r-410 model#dlclrah58aak s#v182346542 going back Monday to Remove charge and recharge with factory charge thanks for any help or advice

  2. #2
    Join Date
    May 2000
    Location
    Indianapolis, IN, USA
    Posts
    40,580
    Post Likes
    Sounds like the place to start. 98 suction on a freezing night is high.

  3. #3
    Join Date
    Nov 2019
    Posts
    5
    Post Likes
    Thread Starter
    Thanks for the reply I'll let you guy know the results

  4. #4
    Join Date
    Jan 2004
    Location
    PA
    Posts
    78,378
    Post Likes
    Moved to Tech to Tech.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  5. #5
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    6,762
    Post Likes
    are you sure it has low ambient control ?

  6. #6
    Join Date
    Nov 2019
    Posts
    5
    Post Likes
    Thread Starter
    I don't know for sure .I call midea tec support and they couldn't help me. because they said it was a carrier unit .so I called are carrier rep and they said it was a midea unit and they could help me .?

  7. #7
    Join Date
    Dec 2007
    Posts
    9,387
    Post Likes
    Not sure of this unit, but midea makes Carrier and Lennox ductless units, if not others.
    The Food Stamp Program, administered by the U.S. Department of Agriculture, is proud to be distributing the greatest amount of free meals and stamps EVER.
    Meanwhile, the National Park Service, administered by the U.S. Department of the Interior, asks us to "Please Do Not Feed the Animals". Their stated reason for this policy "... the animals become dependent on handouts and will not learn to take care of themselves."
    from an excerpt by Paul Jacob in Sun City, AZ

  8. #8
    Join Date
    Nov 2019
    Posts
    5
    Post Likes
    Thread Starter
    Thanks I will try calling Lennox on Monday I think there's a way to set up the low ambient from the condenser but I can't find any manuels on it

  9. #9
    Join Date
    Feb 2019
    Location
    Idaho
    Posts
    5
    Post Likes
    This is a Midea heat pump, the suction would be higher in heat mode, and the coil will freeze and defrost.

  10. #10
    Join Date
    Nov 2019
    Posts
    5
    Post Likes
    Thread Starter
    Thank you for your reply. I guess I forgot to mention we only run unit in cooling mode.it is a kitchen so it's the evaporator that's freezing on cold nights

  11. #11
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    26,129
    Post Likes
    Quote Originally Posted by Rock9806 View Post
    Thank you for your reply. I guess I forgot to mention we only run unit in cooling mode.it is a kitchen so it's the evaporator that's freezing on cold nights
    Sounds like you DON'T have a low ambient control.

    Is this a heat pump?
    Commercial Kitchen?

  12. #12
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,123
    Post Likes
    The low end Daikins have a jumper on the board that you have to cut to enable low ambient operation..... so you need to contact whoever the unit is branded to, or midea down in Florida, and ask them how to enable low ambient operation on your particular model.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI