    Midea or carrier
    Hi guys first time post we installed a midea 5ton mini split in April .system ran good until the weather got cold .now system is freezing at night when temperature drops.I notice condenser fan are running at full speed I thought they would slow down for low ambient control .suction pressure 98 sh 0 slt 30 r-410 model#dlclrah58aak s#v182346542 going back Monday to Remove charge and recharge with factory charge thanks for any help or advice
    Sounds like the place to start. 98 suction on a freezing night is high.
    Nov 2019
    Thanks for the reply I'll let you guy know the results
    Moved to Tech to Tech.
    Virginia
    are you sure it has low ambient control ?
    Nov 2019
    I don't know for sure .I call midea tec support and they couldn't help me. because they said it was a carrier unit .so I called are carrier rep and they said it was a midea unit and they could help me .?
    Not sure of this unit, but midea makes Carrier and Lennox ductless units, if not others.
    Nov 2019
    Thanks I will try calling Lennox on Monday I think there's a way to set up the low ambient from the condenser but I can't find any manuels on it
    Feb 2019
    Idaho
    This is a Midea heat pump, the suction would be higher in heat mode, and the coil will freeze and defrost.
    Nov 2019
    Thank you for your reply. I guess I forgot to mention we only run unit in cooling mode.it is a kitchen so it's the evaporator that's freezing on cold nights
    Southold, NY
    Quote Originally Posted by Rock9806 View Post
    Sounds like you DON'T have a low ambient control.
    Is this a heat pump?
    Commercial Kitchen?
    Southeastern Pa
    The low end Daikins have a jumper on the board that you have to cut to enable low ambient operation..... so you need to contact whoever the unit is branded to, or midea down in Florida, and ask them how to enable low ambient operation on your particular model.