    Help with purging a zone

    I replace the Taco 007-F5 circulator. The old one sounded like a washing machine and was not pumping any hot water. This is a 6 zone Crown boiler and the only issue I have is this one zone. The other 5 zones are doing fine and connected to an air coil in an air handler. This one serves baseboard in the common areas of this office building.

    There is only a dribble of water coming out when I do a power purge on this zone. It has a Taco 218 Flowchek which I suspect is causing the issue. I think the other circ pump got fried to to no water flow.

    The circ pump is on the return side into a return header with the other zones.

    Here are some pics.
    Name:  1.jpg
Views: 153
Size:  99.8 KB

    Name:  2.jpg
Views: 150
Size:  89.1 KB
    Can someone please explain to me -
    Why is there never enough time to do it right the first time, but plenty of time to do it twice?


    Please view site rules: http://hvac-talk.com/vbb/showthread.php?t=1241

    Apply for Pro Membership: http://hvac-talk.com/vbb/showthread.php?t=116113

    Find your local HVAC-Talk Contractor: http://hvac-talk.com/aop

  2. #2
    Join Date
    May 2019
    Posts
    13
    Post Likes
    Is that PRV open to fast fill? Should hear the flow.
    There might be a manual open on the flow check which could be stuck.

  3. #3
    Join Date
    Aug 2015
    Location
    Buffalo,NY
    Posts
    971
    Post Likes
    Number 1 a fill can’t be installed in that position. Now if it were me, I’d lock off every zone that’s working increase boiler pressure and try purging. If you still aren’t getting flow, then I would start looking for the restriction in the line. But once all done, I would re pipe that fill to put it in the horizontal position.


    Sent from my iPhone using Tapatalk

  4. #4
    Join Date
    Dec 2014
    Posts
    2,918
    Post Likes
    I'm betting on a flowcheck issue.
    Have a look inside it.

    Sent from my SM-G950U using Tapatalk

  5. #5
    Join Date
    Sep 2007
    Location
    State College, PA
    Posts
    2,894
    Post Likes
    Thread Starter
    Quote Originally Posted by icy78 View Post
    I'm betting on a flowcheck issue.
    Have a look inside it.

    Sent from my SM-G950U using Tapatalk
    That is what I was thinking. I was wondering if the flow check could be clogged somehow. The water that came out on the purge was real filthy.

    I wnever had a problem with a check valve, wonder if there is a way to adjust it to open more?
    Can someone please explain to me -
    Why is there never enough time to do it right the first time, but plenty of time to do it twice?


    Please view site rules: http://hvac-talk.com/vbb/showthread.php?t=1241

    Apply for Pro Membership: http://hvac-talk.com/vbb/showthread.php?t=116113

    Find your local HVAC-Talk Contractor: http://hvac-talk.com/aop

  6. #6
    Join Date
    Sep 2007
    Location
    State College, PA
    Posts
    2,894
    Post Likes
    Thread Starter
    Quote Originally Posted by Metalman0880 View Post
    Number 1 a fill can’t be installed in that position. Now if it were me, I’d lock off every zone that’s working increase boiler pressure and try purging. If you still aren’t getting flow, then I would start looking for the restriction in the line. But once all done, I would re pipe that fill to put it in the horizontal position.


    Sent from my iPhone using Tapatalk
    Great advice. Thanks. I did not think about shutting off the other zones. That is normally how I do my purge. The baseboards have no bleaders on them.
    Can someone please explain to me -
    Why is there never enough time to do it right the first time, but plenty of time to do it twice?


    Please view site rules: http://hvac-talk.com/vbb/showthread.php?t=1241

    Apply for Pro Membership: http://hvac-talk.com/vbb/showthread.php?t=116113

    Find your local HVAC-Talk Contractor: http://hvac-talk.com/aop

  7. Likes Metalman0880 liked this post
  8. #7
    Join Date
    May 2019
    Posts
    13
    Post Likes
    It takes at least pump pressure to open the flow check. Closing off the other zones might get it to open with fast fill pressure. I have loosened them by exercising the manual open function several times.

  9. Likes Metalman0880 liked this post
  10. #8
    Join Date
    May 2018
    Location
    VA/DC
    Posts
    281
    Post Likes
    did you close the valve under the pump so you can push the water through the baseboard?

  11. #9
    Join Date
    Mar 2015
    Location
    Medford, N.Y.
    Posts
    6,087
    Post Likes
    How much water comes out zone #2 during a purge?

  12. #10
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    25,542
    Post Likes
    You need another Hose Bib on the supply line and a separate pump and bucket too eliminate any air!

  13. #11
    Join Date
    Aug 2015
    Location
    Buffalo,NY
    Posts
    971
    Post Likes
    Quote Originally Posted by pecmsg View Post
    You need another Hose Bib on the supply line and a separate pump and bucket too eliminate any air!
    Why? He said pumps are on the return. Your feeding fresh water on the supply and by the picture you can properly purge any zone on the return while filling. No need for anything additional added on the supply.


    Sent from my iPhone using Tapatalk

  14. #12
    Join Date
    Aug 2015
    Location
    Buffalo,NY
    Posts
    971
    Post Likes
    Looks like on the top of the supply line on the far right there is a coin vent also.

    I go back to my original comment.

    1) re pipe that fill valve correctly.
    2) lock off the other zones and force the water through the zone that’s air bound.
    3) purge said air out
    4)obviously make sure your air eliminator is working.
    5) if the above dose not work figure out what’s stopping your flow.


    Sent from my iPhone using Tapatalk