    That black oil tells me excessive heat probably due to high suction SH and no water jacket!

    6 years old is that the original compressor?

    I see some metal flakes in there , normally (15+ Years) that would be expected but again in a 6 year old pump NO!

    A through investigation MUST be made too find the cause(s) of the failure and correct them!

  2. #54
    Join Date
    Oct 2016
    Location
    Clearwater, Florida
    Posts
    1,557
    Post Likes
    I would think if overheating was a problem, there would be more indicators than that, I don't see any discoloration to where the oil might have been baked on.

    Is the oil is sticky or tacky, I would believe it.

    checking your discharge temps 6" away from the comp on the other comps and seeing if it exceeds 225*F would be a good idea, if it is' then it's cooking the oil.

  3. Likes Wskunza liked this post.
  4. #55
    Join Date
    Mar 2015
    Location
    Medford, N.Y.
    Posts
    6,228
    Post Likes
    Quote Originally Posted by icemeister View Post
    If you can't do the water coil, then add the body cooling fan. If they refuse that, just tell them the compressor manufacturer requires it. If the condensing unit is a Copeland, it originally had one or the other.
    I agree.

    Is there even a "cond fan motor" (body cooling fan) on these comps???

  5. Likes Wskunza liked this post.
  6. #56
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    26,211
    Post Likes
    Quote Originally Posted by TechmanTerry View Post
    I agree.

    Is there even a "cond fan motor" (body cooling fan) on these comps???
    never seen one for the 2 cylinder models!

    I do remember some ice makers installing a small 9W fan by the compressor on water cooled models, don't see how you could adapt in this situation without liability issues!

  7. #57
    Join Date
    Oct 2016
    Location
    Clearwater, Florida
    Posts
    1,557
    Post Likes
    Check the discharge temps, check the suction temps, SH and that'll tell you if it's too hot.

    I know I have a similar one for a freezer but it has a fan on it and is water cooled.

  8. #58
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    26,211
    Post Likes
    Quote Originally Posted by Olivero View Post
    Check the discharge temps, check the suction temps, SH and that'll tell you if it's too hot.

    I know I have a similar one for a freezer but it has a fan on it and is water cooled.
    Little K bodies?

    Iíd like to see that, didnít see anything on Emersonís site for them.

  9. #59
    Join Date
    Jul 2018
    Location
    Las Vegas
    Posts
    91
    Post Likes
    Thread Starter
    Quote Originally Posted by Olivero View Post
    I would think if overheating was a problem, there would be more indicators than that, I don't see any discoloration to where the oil might have been baked on.

    Is the oil is sticky or tacky, I would believe it.

    checking your discharge temps 6" away from the comp on the other comps and seeing if it exceeds 225*F would be a good idea, if it is' then it's cooking the oil.
    Oil wasnít sticky or tacky from what I felt just black as heck still felt viscous. I always check sh subcooling discharge temp. I hear discharge temp + ~75degrees is the temp in the compressor from my reading and understanding and we want to stay under 300f or we will have oil burnoff.


    Sent from my iPhone using Tapatalk

  10. #60
    Join Date
    Jul 2018
    Location
    Las Vegas
    Posts
    91
    Post Likes
    Thread Starter
    Quote Originally Posted by TechmanTerry View Post
    I agree.

    Is there even a "cond fan motor" (body cooling fan) on these comps???
    Nothing except for most casino is open air return but canít really feel a draft stays around 65-70 ambient.


    Sent from my iPhone using Tapatalk

  11. #61
    Join Date
    Mar 2015
    Location
    Medford, N.Y.
    Posts
    6,228
    Post Likes
    Air impingement on the comp body is mandatory for air cooled comps ,I thought. Thats a compressor killer w/o some sort of comp "body cooling",I thought,also.

  12. #62
    Join Date
    Mar 2015
    Location
    Medford, N.Y.
    Posts
    6,228
    Post Likes
    Quote Originally Posted by Wskunza View Post
    Nothing except for most casino is open air return but can’t really feel a draft stays around 65-70 ambient.


    Sent from my iPhone using Tapatalk
    I would give a thought to getting a comp crankcase oil sample from each and every comp and an Acid Test Kit also.

  13. Likes Wskunza liked this post.
  14. #63
    Join Date
    Jul 2018
    Location
    Las Vegas
    Posts
    91
    Post Likes
    Thread Starter
    Also noticed that it look like water/condensation/moisture got into the terminals and possibly created a problem with this unit as the connections look burnt.



    Sent from my iPhone using Tapatalk

  15. #64
    Join Date
    Oct 2016
    Location
    Clearwater, Florida
    Posts
    1,557
    Post Likes
    Quote Originally Posted by Wskunza View Post
    Oil wasn’t sticky or tacky from what I felt just black as heck still felt viscous. I always check sh subcooling discharge temp. I hear discharge temp + ~75degrees is the temp in the compressor from my reading and understanding and we want to stay under 300f or we will have oil burnoff.


    Sent from my iPhone using Tapatalk
    That is correct, according to copeland, 225*F is the MAX MAX MAX discharge temp on the discharge line.

  16. #65
    Join Date
    Oct 2016
    Location
    Clearwater, Florida
    Posts
    1,557
    Post Likes
    Quote Originally Posted by pecmsg View Post
    Little K bodies?

    I’d like to see that, didn’t see anything on Emerson’s site for them.
    This is the model.

    LACA-032E-TAC-800

    Looks similar but I don't think the models similar, it's quite large.