Results 1 to 13 of 20
    Dec 2018
    Ventura, CA
    carrier package unit error code
    Got a Carrier 48GPN030040301. Flashing a 7 code and inducer motor continues to run. Ive pulled the power off and on and it works fine for a day a day or two then its back to the 7 code. High limit? Rollout switch? Ive watched it run through a heat cycle and everything seems good.
    Thanks everyone.
    May 2018
    VA/DC
    7 flashes in a roll out fault. page 14 of the install manual.
    inducer will run on roll outs and high limit trips. Which way is the wind blowing? is it possibly going straight into the flue discharge.
    did you check for a cracked heat exchanger?
    Dec 2018
    Ventura, CA
    No wind. Unit same location for years. Checked burners. Observered flame while blower operating. No flame roll out or agitation.
    No evidence of cracked heat exchanger.
    Virginia
    make sure air filters are clean , and look at the "return" grills in ceilings for caked up dust
    Ive even seen customers shove their own air filters into the grills then forgetting they are in there
    if nothing seen …. replace high limit and roll out …… one of them is going bad , and they are not expensive
    Southeastern Pa
    I was taught many tears ago that the board itself can generate a 7 code, much like the Simplicity board can do with the 9 code.
    It's a roll of the dice if you need a rollout...which is cheap to do. For remote locations where I want to make sure the repair is once-and-done, I quote to replace the board, too.
    2 Tim 3:16-17
    Member, IAEI
    AOP Forum Rules:
    Virginia
    Quote Originally Posted by navyguy1 View Post
    Thanks everyone.
    How old is this unit?
    The induced draft motor “wheels” (small squirrel cage) on these are notorious for rusting out and not pulling enough air into the combustion chamber.
    Sometimes you can look into the exhaust opening (if the shield is missing or corroded) and see the condition of the wheel.
    Southeastern Pa
    That's a good point. I was assuming that he had already looked at the inducer function......
    2 Tim 3:16-17
    Member, IAEI
    AOP Forum Rules:
    Dec 2014
    Possible Burner misalignment.
    Sent from my SM-G950U using Tapatalk
    Dec 2018
    Ventura, CA
    Ok thanks guys. Ok here’s a possible smoking gun. When the weather was hot the ac would lock out as well. Occupant had to turn it off at the breaker and turn it back on.
    May 2018
    VA/DC
    is there a phase monitor or any other safety that an be cutting it off? you need to check all voltage and tighten all the connections an be sure your power supply is solid. start there
    Dec 2018
    Ventura, CA
    Quote Originally Posted by Cool breeze 38 View Post
    No Phase monitor. Ill check the connections. I did blow out the very dirty burner assembly and heat exchanger yesterday. Ill call them and see if its working still. Im leaning toward a bad flame rollout sensor because while it was running I just touched the sensor to see if it was getting hot and it instantly shut down and went into the 7 code.
    Thanks for your input
    Dec 2014
    I don't think they go bad without being subjected to abnormally high heat though. It may not be enough to trip it for a few years but enough to weaken it.
    So there would still be an underlying problem me-thinks.
    Mar 2016
    NY