Results 1 to 10 of 10
    Aug 2010
    York YLAA0100 plate heat exchanger
    Has anyone experienced failures of the plate type heat exchangers in York YLAA 100 ton chillers with under 5 years of service? I have a new customer with multiple chillers that have had these heat exchangers develop leaks allowing freon into the chilled water side.
    Nov 2019
    Dc
    Seen it a few times but I’m the heat recovery side. Never saw the evaporator heat exchanger fail.
    Aug 2019
    LA
    Yes. Usually on variable flow systems. TXV or EEV? There has been some valve replacements to correct issue. New valves are sporlan.
    There are some flow switch changes as well. If you have the Danfoss EEVs there is a software upgrade. There is also a processor software upgrade. If your unit was affected, it should have been upgraded by the local office for free (upgraded txvs are not included).
    if your unit isn’t covered, then I would recommend looking into the Sporlan EEV upgrade and having your flow issues investigated.
    "Right" is not the same as "Wise".
    Nov 2011
    East Side
    They had software and EXV controller issues with a large run of units....hundreds. Your serial number should have been included in the service repair bulletin, and corrected under warranty.
    Aug 2010
    thanks for that information. Is there a place online I can run this serial number to see if this unit is in the group with software and EXV controller issues?
    Quote Originally Posted by my2nd40 View Post
    Not that I am aware of. PM me your serial number.
    dania,fl
    Was the upgrade related to the service bulletin on low pressure trips
    Quote Originally Posted by the wizard View Post
    there were low pressure trip issues, but the main fault was heat exchanger failures.
    Aug 2010
    Quote Originally Posted by jayguy View Post
    I can't pm you can you email me so I can send the serial #
    tomsforty@gmail.com