    Sep 2019
    Cooling Capacity Calculation
    Hello, beautiful people , I've been working on calculating a cooling capacity for freezer stocks , so basically I have two rooms one almost 100 m2 and the other is 1000 m2 at the same height with the same insulation method and storage goods, after doing my calculation the 100 m2 turns out to need a cooling capacity of 44 KW , and the 1000 m2 needs 280 kw. though I was considering 440 kw because nothing has changed except that it's 10 times bigger.
    so my question is, is bigger freezer storage needs less cooling capacity than smaller ones relatively ,or did I made a mistake and should recalculated it !!
    SW FL
    COLD STORAGE WAREHOUSE
    https://www.convertunits.com/from/kw...+refrigeration
    280 kw = 79.62 tons
    1000 m^2 = 10,764 SQ FEET
    Seems like more than Adequate.
    However, Height is not provided.
    WAREHOUSE FREEZER.
    PRODUCT ?
    PRODUCT TEMPERATURE when put in freezer?
    AMBIENT Temp. ?
    Designer Dan
    Sep 2019
    Well both of them at the same height of 8 meter , to store frozen vegetables , inlet goods temperature is approximately not least than -12 C , at an ambient of 38 C .