    Quote Originally Posted by VTP99 View Post
    Why would pulling the blower door off a sealed combustion change anything.
    Is it not a sealed combustion unit ?
    Maybe you can help me understand it. Also it was when i pulled the top door with the burners,inducer motor, gas valve e.t.c.
    Im definitely open to ideas. All i know is when i left the door open it would run fine, door closed it wouldnt. Flue kit opened and no inner liner. This made me think the recycling of the co was somehow affecting it running correctly. Ideas?

  2. #15
    Join Date
    Dec 2002
    Location
    SouthEast NC ICW & Piedmont Foothills
    Posts
    7,900
    Post Likes
    Unless that is the exterior wall?
    "This accessory must be used only for terminating the vent of a Category IV furnace. Do not use this termination kit for any other type furnace. Failure to follow this warning could result in fire, personal injury or death."
    It`s better to be silent and thought the fool; than speak and remove all doubt.

  3. #16
    Join Date
    May 2017
    Location
    richmond virginia
    Posts
    47
    Post Likes
    Thread Starter
    Quote Originally Posted by dandyme View Post
    Unless that is the exterior wall?
    "This accessory must be used only for terminating the vent of a Category IV furnace. Do not use this termination kit for any other type furnace. Failure to follow this warning could result in fire, personal injury or death."
    Yes it is the exterior wall

  4. #17
    Join Date
    Jan 2010
    Posts
    18,579
    Post Likes
    Does the termination have this on the end outside ?
    Attached Images Attached Images  

  5. #18
    Join Date
    May 2017
    Location
    richmond virginia
    Posts
    47
    Post Likes
    Thread Starter
    Quote Originally Posted by VTP99 View Post
    Does the termination have this on the end outside ?
    No it does not. its just straight up pvc. Ill be going back this week and will have more pics but as as the other day, nothing

  6. #19
    Join Date
    Mar 2016
    Location
    Dayton Oh
    Posts
    2,139
    Post Likes
    Quote Originally Posted by VTP99 View Post
    Why would pulling the blower door off a sealed combustion change anything.
    Is it not a sealed combustion unit ?
    It’s not sealed combustion in the way that trane carrier and Lennox do it. Goodman burners are open to the entire half of the furnace. So there is not a sheet metal box enclosing the burners. The pipe just goes into the half of the furnace to give it its combustion air.

    So with the door off it is pulling air from the room. Door on pulling from pipe.


    Sent from my iPhone using Tapatalk

  7. #20
    Join Date
    Jan 2010
    Posts
    18,579
    Post Likes
    Quote Originally Posted by jbhenergy View Post
    It’s not sealed combustion in the way that trane carrier and Lennox do it. Goodman burners are open to the entire half of the furnace. So there is not a sheet metal box enclosing the burners. The pipe just goes into the half of the furnace to give it its combustion air.

    So with the door off it is pulling air from the room. Door on pulling from pipe.


    Sent from my iPhone using Tapatalk
    I understand that but the blower compartment and the combustion are separated. He said pulling the blower allowed the unit to run.
    Attached Images Attached Images   

  8. #21
    Join Date
    May 2017
    Location
    richmond virginia
    Posts
    47
    Post Likes
    Thread Starter
    Quote Originally Posted by VTP99 View Post
    I understand that but the blower compartment and the combustion are separated. He said pulling the blower allowed the unit to run.
    Not the blower door. The burner door. I clarified a few posts ago. Sorry for the confusion vtp99

  9. #22
    Join Date
    Jul 2000
    Location
    Northern Wisconsin
    Posts
    3,076
    Post Likes
    The installer probably didn't glue the inside pipe to the "wye" and it and the outside termination fell out. Someone that didn't know what they were dealing with tried to put it back together (outside) and when it didn't want to go back together right figured out if they took the 2" pipe off the "cap" fit back on just fine.

    Kind of hard to see down into one of those from outside, try a bore scope. If there is a hub for 2" to fit into from outside, put a new length of 2" and fix the situation.
    Use the biggest hammer you like, pounding a square peg into a round hole does not equal a proper fit.

  10. #23
    Join Date
    May 2017
    Location
    richmond virginia
    Posts
    47
    Post Likes
    Thread Starter
    This is how it would run. With this door off
    Attached Images Attached Images  

  11. #24
    Join Date
    Jan 2010
    Posts
    18,579
    Post Likes
    [QUOTE=kennybaker2014;25809115] Push in door switch and on it comes. Tape the switch closed and watch for a few minutes. Eventually i go to close door and it immediately goes out. I open it up and push switch and everything's fine again. Only when i close door is it not working. /QUOTE]

    The switch is on the blower section. Something is not adding up.
    Attached Images Attached Images  

  12. #25
    Join Date
    May 2017
    Location
    richmond virginia
    Posts
    47
    Post Likes
    Thread Starter
    [QUOTE=VTP99;25809207]
    Quote Originally Posted by kennybaker2014 View Post
    Push in door switch and on it comes. Tape the switch closed and watch for a few minutes. Eventually i go to close door and it immediately goes out. I open it up and push switch and everything's fine again. Only when i close door is it not working. /QUOTE]

    The switch is on the blower section. Something is not adding up.
    Yes youre right. I said door as opposed to doorS. To be precise i removed doorS. Once doorS were removed i pushed furnace switch. When i saw it ran i put doorS back on. It went out once again. As i removed burner DOOR it came again and ran fine. When it ran fine i only had the burner DOOR off.

  13. #26
    Join Date
    Jul 2019
    Posts
    21
    Post Likes
    Quote Originally Posted by VTP99 View Post
    Why would pulling the blower door off a sealed combustion change anything.
    Is it not a sealed combustion unit ?
    It's sealed combustion with the door closed, when it's open it's just going to take the room air. So if the door is closed and the concentric vent is hooked up improperly, it's gonna be sucking the flue gasses instead of fresh air