Results 1 to 13 of 18
    Nov 2019
    Only getting 1/2 of the 28 VAC from the transformer
    43 year old air handler (apartment maintenance) , only getting 14vac in the unit.
    Reading 28vac at the transformer. Replaced the T-Wire from the tstat to the air handler . . . still getting 1/2 of the supplied low voltage available
    Oct 2011
    Chicagoland Area
    So what is your question? You are losing voltage somewhere....Figure out where you are losing voltage and you have figured out your problem.
    Nov 2019
    I thought it was odd to loose exactly 50% of what I should be reading on my meter
    Oct 2011
    Chicagoland Area
    You are either losing voltage or have phantom voltage at your load.
    Tucson, Arizona
    Where are you reading 14v at, terminal strip at air handler from C to R? Is common grounded? What do you get from R to common at transformer? And from R at the terminal strip to cabinet ground? Do you have continuity from common terminal of transformer to ground wire at cabinet ground? What’s the power into the A/H, is it on the proper transformer terminal (208?)
    That’s about where I’d start my readings to figure out where it went wrong
    There are two ways to do things, Right and Again.
    Oct 2011
    Gladstone, Oregon (Portland)
    New tech?
    edmonds wa
    That old of air handler should be replaced, but it should be easy to trouble shoot. Leave one lead on xfmr common and use the other to follow the circuit around.
    UA Local 32 retired as of Jan 2020
    Nov 2019
    Buford! Thank You ! I traced the xformer 28vac to the outside condenser contactor . . .wire biodegraded and grounding but not kill'n the xformer, "and" the one time resistor fuse was blown on one of the heat strips 😅👍🏻
    Quote Originally Posted by Dirt Farm View Post
    Buford! Thank You ! I traced the xformer 28vac to the outside condenser contactor . . .wire biodegraded and grounding but not kill'n the xformer, "and" the one time resistor fuse was blown on one of the heat strips ������
    That's not a resister. Its a thermal fuse. To protect from over heating and starting a fire.
    Nov 2019
    Ty been there, it looks like a resistor to me? :-)
    Nov 2019
    I went through basic electricity and electronics in the USN in 1982 😅
    Virginia
    There are no resistors in heat strips ….. just a thermal fuse (that looks very much like a resistor) that cuts power when it gets too hot
    May 2014
    Bay Area California
    But, but, but . . . Isn't the heat strip itself a resistor?
    Quote Originally Posted by Snapperhead View Post
    I do a triple evac with nitro to remove non condensables.