    duct design ?

    PD of wet coil =.27
    PD of 4" honeywell f100 merv 11 filter cabinet = .23

    my math tells me i have 0 ASP for my duct.

    WTF.

    suggestions to go from here. C width coil vs B width?

  2. #2
    Join Date
    Nov 2006
    Location
    Athens, Ohio
    Posts
    7,003
    Post Likes
    How about a MERV 8? I have found that can make a difference.
    AOP Rules: Rules For Equipment Owners.

    Free online load calculator: http://www.loadcalc.net/


    There = not here. Their = possessive pronoun. They're = they are
    It's = contraction of it is. Its = the possessive form of it
    Too = also. To = expressing motion. Two = 2
    Then = after that, next. Than = indicates a comparison.
    Questions should end with a question mark "?" Statements end with a period "."

  3. #3
    Join Date
    Jul 2019
    Location
    Oklahoma home its in the name
    Posts
    532
    Post Likes
    I don't know your situation but if there's like two returns off of the return plenum then you could put two filter racks to reduce the static. Or my favorite is to use multiple return filter grills. The only problem is that usually restricts you to either one or two inch filters.

    Sent in a state of increasing entropy using Tapatalk

  4. #4
    Join Date
    Mar 2018
    Location
    Kansas Flatlands
    Posts
    364
    Post Likes
    Quote Originally Posted by R600a View Post
    I don't know your situation but if there's like two returns off of the return plenum then you could put two filter racks to reduce the static. Or my favorite is to use multiple return filter grills. The only problem is that usually restricts you to either one or two inch filters.

    Sent in a state of increasing entropy using Tapatalk
    Filter grills are restrictive be careful there

  5. #5
    Join Date
    Jul 2019
    Location
    Oklahoma home its in the name
    Posts
    532
    Post Likes
    Yes but if you have multiple you can get the static pretty low by having more filter area.

    Sent in a state of increasing entropy using Tapatalk

  6. #6
    Join Date
    Mar 2014
    Location
    Grand Blanc
    Posts
    550
    Post Likes
    Why not pick a less restrictive filter? I use the following budget to pick my filters, coils and size ductwork.

    Coil PD max 2.5”
    Filter PD max 1.5”
    Supply Duct .05”
    Return Duct .05”

    If I’m limited on ductwork then I’ll pick a less restrictive filter or over size the coil cabinet.


    Sent from my iPhone using Tapatalk

  7. #7
    Join Date
    Mar 2016
    Location
    Dayton Oh
    Posts
    1,999
    Post Likes
    Thread Starter
    Actually everyone, I just can’t read......

    Name:  IMG_3538.png
Views: 95
Size:  188.6 KB

    If I could read, I would have seen that running a 16x25 at 1200 cfm then my pd is like .175 across the filter.

    Back to the calculator......

    What a dumb dumb.


    Sent from my iPhone using Tapatalk