    10 ton trane package unit

    Hello everyone, My name is Terry, I'v been a tech for a couple years now, nice to meet everyone.

    I was needing some help with a trane 10 ton heat pump package unit I'm working on Model WSC120E. The unit has proper charge and runs great in cool mode no problems there, when the unit is switched into heat mode my second circuit pulls a vacuum on the low side and trips the low pressure cutout, it also freezes after the txv and distributing lines leading into the outdoor coil. While it is frozen up I tried to put the sensing bulb in hot water to open up the valve and but it stays frozen do I have a bad txv or is there something else I should be checking, thanks ahead of time for and advice.

  2. #2
    Join Date
    Jan 2012
    Location
    Missouri, USA
    Posts
    1,503
    Post Likes
    Sounds like a txv issue to me. Get your post count up and apply for Pro membership, it’s free and you get lots of good training info.

  3. Likes CEAS-AC-TECH liked this post
  4. #3
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,058
    Post Likes
    Did you confirm the charge is correct while in cooling mode?
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  5. #4
    Join Date
    Nov 2019
    Posts
    4
    Post Likes
    Thread Starter
    Yes the charge is correct in cooling mode, checked with subcooling charging curve chart from the unit manual.

  6. #5
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,058
    Post Likes
    In that case I would probably agree with ksefan.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  7. #6
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,058
    Post Likes
    Full disclosure: I haven't touched a Trane heat pump RTU in probably 11 or 12 years.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  8. #7
    Join Date
    Sep 2007
    Location
    edmonds wa
    Posts
    4,426
    Post Likes
    Is that a danfoss valve brazed onto the dist body and the real skinny cap tube line to bulb?
    UA Local 32 retired as of Jan 2020

  9. #8
    Join Date
    Nov 2019
    Posts
    4
    Post Likes
    Thread Starter
    It doesn't say Danfoss on the powerhead but when I type in its number online a Danfoss page is one of the first that shows up, it does have a very small line to the bulb the line doesn't appear to be kinked or damaged, same for the bulb. It also has an external equalization line.

  10. #9
    Join Date
    Nov 2019
    Posts
    4
    Post Likes
    Thread Starter
    Hello everyone, just so this might be of some help to people in the future I wanted to give this thread a resolution. I replaced the TXV and the unit runs great now in cool and heat mode, also replaced the dryer. Thanks again to everyone for the help.

  11. #10
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,058
    Post Likes
    Thanks for the closure....we appreciate it.