Results 1 to 11 of 11
    Jun 2013
    Goodman heat pump
    Hello friends Im working on a Goodman heat pump less than 3 months since installed
    It runs good for hours then it blows the 3 amp board fuse in air handler
    Unable to verify the over amp or short
    Any ideas
    Mar 2018
    Florida
    I can only say things like that can take a while. time to get out a meter.
    May 2018
    Elizabethtown, PA
    Is it being used for heating or cooling? Does the fuse blow in both modes? What measurements have you taken?
    If this is happening in heat only, I wouldn't be surprised if there is a short in the defrost wiring.
    Jun 2013
    Yes heating, cooling is fine
    Im suspecting defrost wiring too trying to catch it
    May 2018
    FLORIDA
    Quote Originally Posted by ARIOSTO1 View Post
    Hello friends I’m working on a Goodman heat pump less than 3 months since installed
    Any ideas
    Check Thermostats and contactor, sometime low voltage short come from there
    also check thermostat wires, especially inside condenser and air handler,
    sometime they touch the metal cabinet
    Visit our website at www.airconcomfortcooling.com
    Jan 2012
    Missouri, USA
    Did the forced defrost work?
    Jun 2013
    The white wire from airhandler to condenser was pulling 6.5 amps l just switched with another wire and when back to 0.3 amps
    Great!!
    Jan 2014
    New England
    Sounds like you got it, time will tell..BTW, if this is on a residential property hopefully the owner registered the system as manufacturers warranty decreases significantly if never registered. California and Quebec need not to be registered to receive the maximum manufacturers warranty.
    May 2018
    FLORIDA
    you got it
    edmonds wa
    So the white wire is shorted somewhere? i would pull up a chair and run it thru all cycles a couple times.
    UA Local 32 retired as of Jan 2020
  11. Likes CEAS-AC-TECH liked this post
  12. #11
    Southold, NY
    Great!!
    Do you realize how lucky you are extra wires were pulled!
  13. Likes CEAS-AC-TECH liked this post