Thread: Honeywell ssv

  1. #1
    Join Date
    Nov 2019
    Posts
    2
    Post Likes

    Honeywell ssv

    Looking for help on an issue Im having with a make up air unit. Unit staying on low fire. Gas pressure going into ssv is 15wc then goes through 2 Honeywell fluid filled gas valves and comes out at 5wc. There is red fluid in both actuators and shaft does go from shut to open. Then gas flow goes through Honeywell modulating gas valve which does operate and is calling for hi fire. Would replacing the actuator heads fix the problem?

  2. #2
    Join Date
    Nov 2004
    Location
    up in the hizzy
    Posts
    3,436
    Post Likes
    is this some sort of joke?
    There is not better place for the working men than the union! 100% UA the only HVAC union!

  3. #3
    Join Date
    Nov 2019
    Posts
    2
    Post Likes
    Thread Starter
    Whats wrong with the question?