    Sep 2010
    Indiana
    BQ Cartridge Selection
    Hello,
    I have had a BQ kit for some time but have never needed it.
    I am putting one on a small cooler. 4600 BTU R22.
    AAA Cartridge is 1/8 - 1/3 ton (1500 - 4000)
    AA Cartridge is 1/2 - 2/3 ton (6000 - 8000)
    Do I round up or round down?
    Thanks!
    Jul 2019
    Oklahoma home its in the name
    Sorry for the elementary question but what is a BQ cartridge?
    Sent in a state of increasing entropy using Tapatalk
    Sep 2010
    Indiana
    Quote Originally Posted by R600a View Post
    Sporlan TXV kit. You build it from a body, power element, and cartridge to fit your need.
  4. Likes R600a liked this post.
  5. #4
    Aug 2013
    Omaha
    A. When in doubt, pick the smaller size. Itll throttle better and you wont have hunting from too big of a valve.
    B.. remember refrigerant choice matters in picking cartridge size. Sporlan has a chart for which size to use. Compare r12/134a to r22 or 404a. Quite a difference
    Sent from my SM-G975U using Tapatalk
  6. Likes VanMan812 liked this post.
  7. #5
    Jan 2010
    Sea to Sky
    Stop guessing and follow Sporlan's selection criteria.....Bulletin 10-10
    https://www.google.ca/url?sa=t&sourc...LvJXknyblNxsZI
    Sent from my SM-G965W using Tapatalk
  8. Likes icemeister, UmmScott liked this post.
  9. #6
    Jul 2000
    Guayaquil, EC
    The BQ AAA cartridge should work well. If you go to Bulletin 10-10 and do the recommended selection procedure you'll find the corrected capacity is often higher than the nominal capacity of the cartridge.
    In this instance, since you have a small cooler with a R22 compressor capacity of 4600 Btuh, I''ll assume a 20F evaporator temperature and 110F liquid temperature and 200 psi available pressure drop across the TXV.
    NOTE: If the evaporator has a distributor you need to deduct the pressure drop of the distributor nozzle and the distributor tubes which would be approximately 35 psi. In this case however, the capacity is too low to require a distributor.
    The nominal capacity for a AA cartridge is listed as .38 tons, the liquid temperature correction factor is .94 and the pressure drop factor is 1.26, so multiplying those out I get a corrected capacity of .45 tons or 5400 Btuh.