    The tech bypassed the start cap? For what?

  2. #15
    Join Date
    Nov 2019
    Posts
    12
    Post Likes
    Thread Starter
    I was asking if the Hard Start could be bad, so I think he bypassed it to see if there was a difference.

    Ive had the power to my outside unit OFF for 5 hours. Outside temp is 35 degrees. I just turned the power on. The compressor may have run a few more seconds longer than before, but it still shut off after 7 seconds or so.

    Looking like Ill need to get a second opinion.

  3. #16
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    26,199
    Post Likes
    Quote Originally Posted by ntx_homeowner View Post
    I was asking if the Hard Start could be bad, so I think he bypassed it to see if there was a difference.

    Ive had the power to my outside unit OFF for 5 hours. Outside temp is 35 degrees. I just turned the power on. The compressor may have run a few more seconds longer than before, but it still shut off after 7 seconds or so.

    Looking like Ill need to get a second opinion.
    and maybe a 3rd

  4. #17
    Join Date
    Jul 2011
    Location
    DFW, TX.
    Posts
    1,481
    Post Likes
    Quote Originally Posted by ntx_homeowner View Post
    Thanks for your reply! It seems to me that it is actually running for about 5 seconds, then failing. Here is a video of it I just took.

    youtu.be/jXBePbe20Ds
    Please fix this link as its broken up.

    Sent from my LG-G710 using Tapatalk

  5. #18
    Join Date
    Jul 2011
    Location
    DFW, TX.
    Posts
    1,481
    Post Likes
    Quote Originally Posted by ntx_homeowner View Post
    I was asking if the Hard Start could be bad, so I think he bypassed it to see if there was a difference.

    Ive had the power to my outside unit OFF for 5 hours. Outside temp is 35 degrees. I just turned the power on. The compressor may have run a few more seconds longer than before, but it still shut off after 7 seconds or so.

    Looking like Ill need to get a second opinion.
    Given your username you should not have an issue finding a good company if you follow what i said in my earlier post.

    Sent from my LG-G710 using Tapatalk

  6. #19
    Join Date
    Nov 2019
    Posts
    12
    Post Likes
    Thread Starter
    Thanks to everyone for the helpful replies!

  7. #20
    Join Date
    Sep 2007
    Location
    State College, PA
    Posts
    2,970
    Post Likes
    I am pretty sure I what this is as I have seen the exact same thing on a Trane system.

    What you need is a technician that knows what he/she is doing and understands your system.

    Start calling before you spend a pile of money on the wrong cure.
    Can someone please explain to me -
    Why is there never enough time to do it right the first time, but plenty of time to do it twice?


    Please view site rules: http://hvac-talk.com/vbb/showthread.php?t=1241

    Apply for Pro Membership: http://hvac-talk.com/vbb/showthread.php?t=116113

    Find your local HVAC-Talk Contractor: http://hvac-talk.com/aop

  8. Likes CEAS-AC-TECH liked this post.
  9. #21
    Join Date
    Oct 2016
    Location
    Clearwater, Florida
    Posts
    1,557
    Post Likes
    Yeah, sounds like a safety going out.

    Bypassing a hard start makes no sense, replacing one to see if the old one was bad I could understand, the compressor won't start without a hard start or start capacitor.

  10. Likes CEAS-AC-TECH liked this post.
  11. #22
    Join Date
    Nov 2019
    Posts
    12
    Post Likes
    Thread Starter
    Thanks joemach and olivero!

    Joemach, since you have seen this issue before, any advice on what specifically I should ask the next technician? I am going to call around this morning, but I'd like some type of litmus test to be sure they know what they are talking about before spending the money on another service appointment.

  12. #23
    Join Date
    Nov 2019
    Posts
    12
    Post Likes
    Thread Starter
    It is currently 27 degrees outside. I just turned the power back on to my system. I got a much longer compressor startup this time, but it still failed. Here is a video of this morning's startup:

    https://youtu.be/2mEBbTtFfsI

    I have very limited knowledge of how these things work, but based on the fact that the run time increases after leaving it in the cold overnights, does that point to what Olivero is saying — a bad safety?

  13. #24
    Join Date
    Nov 2006
    Location
    Athens, Ohio
    Posts
    7,207
    Post Likes
    A cycle that short will reveal nothing about refrigerant pressures. All of those "OK" findings don't tell us anything as they are not measurements. You need a more capable technician.
    AOP Rules: Rules For Equipment Owners.

    Free online load calculator: http://www.loadcalc.net/


    There = not here. Their = possessive pronoun. They're = they are
    It's = contraction of it is. Its = the possessive form of it
    Too = also. To = expressing motion. Two = 2
    Then = after that, next. Than = indicates a comparison.
    Questions should end with a question mark "?" Statements end with a period "."

  14. #25
    Join Date
    Sep 2008
    Location
    VA
    Posts
    3,729
    Post Likes
    What did it do when the tech bypassed the start cap? Did it run for a few seconds, or not at all?
    "The only true wisdom is in knowing you know nothing" Socrates

  15. #26
    Join Date
    Sep 2007
    Location
    State College, PA
    Posts
    2,970
    Post Likes
    Quote Originally Posted by mgenius33 View Post
    What did it do when the tech bypassed the start cap? Did it run for a few seconds, or not at all?
    I am real curious as to how the tech bypassed the start components.
    Can someone please explain to me -
    Why is there never enough time to do it right the first time, but plenty of time to do it twice?


    Please view site rules: http://hvac-talk.com/vbb/showthread.php?t=1241

    Apply for Pro Membership: http://hvac-talk.com/vbb/showthread.php?t=116113

    Find your local HVAC-Talk Contractor: http://hvac-talk.com/aop

Page 2 of 3 FirstFirst 123 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •