    HEATPIPS in FAHU

    The FAHU that is around above 200-ton capacity with 4 number consist heat recovery and heat pipe. We face a problem that ahu room where no space to remove the giant heat pipe to service and the 6-row cooling coil which trapped inside the heat pipe. The ahu is working without service the cooling coil from last 10 year. Some people opined that eliminate the heat pipe, because already system has heat recovery. heat pipe only will slightly maintain RH and it is trivial. And will get more space to service the cooling coil. What are your comments. Thanks
    Attached Images Attached Images  

  2. #2
    R600a's Avatar
    R600a is offline Professional Member*/Membership Committee
    Join Date
    Jul 2019
    Location
    Hanging out with the mice behind the fridge talking bad about the roaches in the oven.
    Posts
    31,872
    Post Likes
    Well i cant say i really understand your situation but i am certainly interested.
    What does the heat pipe do? Is it setup to help control humidity by bypassing sensible heat around the coil? If so than it seems from my research that you would be marginally increasing the system sensible capacity while decreasing the latent capacity if you remove it.
    I would start by asking my self if i can afford the reduction in latent capacity.
    Also will the increased sensible capacity cause short cycling or worsen it?
    Was it installed because of a specific need for it or was it just a salesman making more profit on unnecessary add-ons?

    I have to say that you always have the most interesting questions.

    Sent in a state of increasing entropy using Tapatalk
    "Is this before or after you fired the parts cannon at it?" - senior tech
    I'm tired of these mediocre "semi flammable" refrigerants. If we're going to do it let's do it right.
    Unless we change direction we are likely to end up where we are going.
    "It's not new, it's better than new!" Maru.

  3. #3
    Join Date
    Feb 2008
    Location
    Dubai
    Posts
    901
    Post Likes
    Thread Starter
    This is a combination of pre cool and reheat process by which change the saturated condition of air off temperature. RH will only be varied by this arrangement.
    Attached Images Attached Images  

  4. #4
    R600a's Avatar
    R600a is offline Professional Member*/Membership Committee
    Join Date
    Jul 2019
    Location
    Hanging out with the mice behind the fridge talking bad about the roaches in the oven.
    Posts
    31,872
    Post Likes
    Exactly just a different way of saying it. You're basically taking sensible heat and bypassing it around the coil. So that the coil can remove more moisture.

    Sent in a state of increasing entropy using Tapatalk
    "Is this before or after you fired the parts cannon at it?" - senior tech
    I'm tired of these mediocre "semi flammable" refrigerants. If we're going to do it let's do it right.
    Unless we change direction we are likely to end up where we are going.
    "It's not new, it's better than new!" Maru.

  5. #5
    Join Date
    Feb 2008
    Location
    Dubai
    Posts
    901
    Post Likes
    Thread Starter
    I put the manufacture’s documented typical design value in psychrometric then I found only a very little arounf 0.91lb(w)/lb moisture content (absolute humidity) removed by the pre cool coil. but the RH maintains 60% after the reheat coil.
    Attached Images Attached Images  

  6. #6
    Join Date
    Feb 2006
    Location
    Float'N Vally, MS
    Posts
    3,521
    Post Likes
    We are in a very humid area that is also hot in the summer.
    I have seen "0" heat pipes here. Now my brother is in a cooler climate and puts them in regularly.
    IMHO they seem to be one step above snake oil... Not worth the (install) money or aggravation.
    Life is too short, Behappy!
    TFMM

  7. #7
    Join Date
    Feb 2008
    Location
    Dubai
    Posts
    901
    Post Likes
    Thread Starter
    Quote Originally Posted by behappy View Post
    We are in a very humid area that is also hot in the summer.
    I have seen "0" heat pipes here. Now my brother is in a cooler climate and puts them in regularly.
    IMHO they seem to be one step above snake oil... Not worth the (install) money or aggravation.
    I align with you, after the psychometric analysis, i thing there is not much benefit from heat pipe. really welcome if any different comments and more lights to the subjects

  8. Likes R600a liked this post.
  9. #8
    R600a's Avatar
    R600a is offline Professional Member*/Membership Committee
    Join Date
    Jul 2019
    Location
    Hanging out with the mice behind the fridge talking bad about the roaches in the oven.
    Posts
    31,872
    Post Likes
    Keep us posted.
    If you do remove it i would love to see before and after refrigerant saturation temps and dew points of supply and return air.

    Sent in a state of increasing entropy using Tapatalk
    "Is this before or after you fired the parts cannon at it?" - senior tech
    I'm tired of these mediocre "semi flammable" refrigerants. If we're going to do it let's do it right.
    Unless we change direction we are likely to end up where we are going.
    "It's not new, it's better than new!" Maru.

  10. #9
    Join Date
    Sep 2019
    Location
    Northern Ontario
    Posts
    90
    Post Likes
    Interested in this. Wouldn't the benefit be the energy saving from the easier cooling and moisture removal by the cooling coil? I see the "free" reheat temperature rise after the coil and think less natural gas or electric reheat.

    You are transfering the energy you want around the cooling coil instead of making the cooling coil remove this energy, then adding energy after coil?

  11. #10
    R600a's Avatar
    R600a is offline Professional Member*/Membership Committee
    Join Date
    Jul 2019
    Location
    Hanging out with the mice behind the fridge talking bad about the roaches in the oven.
    Posts
    31,872
    Post Likes
    It seems like a desuperheater type setup would be more efficient than the heat pipe anyway because it could help lower head pressure.

    Sent in a state of increasing entropy using Tapatalk
    "Is this before or after you fired the parts cannon at it?" - senior tech
    I'm tired of these mediocre "semi flammable" refrigerants. If we're going to do it let's do it right.
    Unless we change direction we are likely to end up where we are going.
    "It's not new, it's better than new!" Maru.

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •