Results 1 to 13 of 13
    Windsor area Ontario Canada
    Carrier Edge dropping out when limit opens new install
    Just had installers install new 96% 2 stage carrier downflow with new AC and edge thermostat. Customer called few days later because of no heat, found it going off on limit, gas pressure wasn't adjusted properly by installers but is now good (1.3"wc 1st stage , 3.5"wc 2nd stage) but was still going off on limit, found duct issues in crawl space we are fixing on Monday but customer noticed whenever furnace went off on limit the thermostat went blank, carrier edge stat, the one with 2 wires from stat to control module (Vg & V+) and 5 wires from control wire to furnace (r,w,y,g,c)
    Just wondering if anyone has ever seen this before?
    This furnace is doing strange things and I plan to go there monday, they also said there was a bunch of smoke coming from furnace because blower didn't start, my tech went there and no smoke and blower started everytime.
    Any ideas on either of these? I have never heard of a limit dropping power to thermostat, i will update info on monday when i look for myself.
    Cincinnati, Oh
    A lot of furnaces do that.
    It’s a way to let the customer know there is something wrong, because otherwise it would go unnoticed.
    I've honestly never seen it before and i have been in the trade for 15 years, is it just communicating stats that do this?
    Cincinnati, Oh
    Quote Originally Posted by markmast View Post
    nope.
    One I can think of specifically would be Tempstar/ICP products. Cant remember the model, but the ones that have the stainless steel front covers.
    Some older Janitrols would do the same thing.
    It just kills R out of the board.
    "Just get it done son."
    Dad adjusted
    Carrier does that. Drops R when the limit opens. Why is the limit opening? Oversized furnace comes to mind.
    No.
    As you can see from the attached wiring diagram, 24 volts from the transformer passes through the limit and Rollout switches before going to the “R” terminal on the furnace control board.
    If that “R” terminal loses 24 volts because any of those limits are “OPEN”, the control module will lose power, and subsequently the thermostat will lose power.
    Thank you for the input, appreciate it,
    It is going off on limit because the duct work is restricted, i am not sure how the old one worked but the return is just a box in the crawl with 2 - 6" flexs over to 2 returns in the house, definitely not enough, and one of those returns were covered by furniture when my tech went there. Also the supplies all had media filter stuffed in them, restricting air flow and the supply has a piece of 12" flex in between 2 pieces of rectangle duct so there is a few things we need to address here.
    Maybe the smoke was the oil burning off.
    Mar 2017
    ORE.
    Poor air flow
    Gotta be a ductwork issue. Test static?
    Replace like for like BTU wise?
    Sent from my iPad using Tapatalk
    Aug 2009
    Rhode Island
    A lot of furnaces drop R especially older ones, see it a lot when customers want wifi tstats and they wont always work
    Dec 2019
    Had one do the same thing and found little air filters in every outlet and the return air duct also had a filter on the inside. Customer figured it would keep the dust to a minimum.
    edmonds wa
    Proper start up and test would have caught all those issues before the customer found them.
    UA Local 32 retired as of Jan 2020
    Mar 2015
    Tx
    Yep they do.
    Doesn't anyone read the dang books that come with new equipment ?