Results 1 to 13 of 20
    Oct 2018
    Trane XV18 problem
    Any advice would be welcome before I start off on the wrong track....
    On startup the refrigerant pressure drops to 40 psi and then system switches off. There is a slight rattle in the compressor just before it stops. Thermostat shows error code 161.01 which is not in the error code list we have.
    We are thinking that maybe there is a blockage in the refrigerant line. Already swapped the expansion valve in the air handler with no effect. I uploaded a video:
    Video: https://youtu.be/ZMdPhVEkQ1k
    What do you guys think?
    Jul 2011
    DFW, TX.
    Did you guys ever actually check the evap coil to see if its clogged? That r22?
    Sent from my LG-G710 using Tapatalk
    Nov 2019
    ERR161.01 is an EEV gas temp sensor error. Is this a heat pump or Cooling only unit? Are you having this issue in heating mode or cooling mode?
    Jul 2011
    DFW, TX.
    Quote Originally Posted by MichaelBaker View Post
    Oct 2011
    Culver, Oregon (Central OR)
    That looks like an XV2
    Oct 2018
    This is a cooling unit only.
    Oct 2018
    XV18
    Southold, NY
    Why is it orange?
    Oct 2018
    The units have bee painted with Heresite for corrosion protection!
    Nov 2019
    So cooling only unit, with an ERR161.01, your gas temp sensor on the air handler is not reading correctly which is causing the EEV to close. OHM out the sensor and see what it is reading. Run fan only without compressor and compare your resistance reading to return air temp. Should obviously be the same.
    Might want to see what he head pressure is doing.
    Aug 2009
    Beatrice, NE
    If the stat is showing an alert code then the CDA on the air handler should be showing one also.
    I would try to manually open the EEV and see what happens, You can also see what position the EEV is in through the CDA. I would walk through the monitor menu to see what it is reporting.
    Jun 2006
    Victoria, Texas
    Check the sensor at air handler.
Contracting Business
HPAC Engineering
EC&M
CONTRACTOR