    Trane XV18 problem

    Any advice would be welcome before I start off on the wrong track....

    On startup the refrigerant pressure drops to 40 psi and then system switches off. There is a slight rattle in the compressor just before it stops. Thermostat shows error code 161.01 which is not in the error code list we have.

    We are thinking that maybe there is a blockage in the refrigerant line. Already swapped the expansion valve in the air handler with no effect. I uploaded a video:

    Video: https://youtu.be/ZMdPhVEkQ1k

    What do you guys think?

  2. #2
    Join Date
    Jul 2011
    Location
    DFW, TX.
    Posts
    1,387
    Post Likes
    Did you guys ever actually check the evap coil to see if its clogged? That r22?

    Sent from my LG-G710 using Tapatalk

  3. #3
    Join Date
    Nov 2019
    Posts
    2
    Post Likes
    ERR161.01 is an EEV gas temp sensor error. Is this a heat pump or Cooling only unit? Are you having this issue in heating mode or cooling mode?

  4. #4
    Join Date
    Jul 2011
    Location
    DFW, TX.
    Posts
    1,387
    Post Likes
    Quote Originally Posted by MichaelBaker View Post
    Any advice would be welcome before I start off on the wrong track....

    On startup the refrigerant pressure drops to 40 psi and then system switches off. There is a slight rattle in the compressor just before it stops. Thermostat shows error code 161.01 which is not in the error code list we have.

    We are thinking that maybe there is a blockage in the refrigerant line. Already swapped the expansion valve in the air handler with no effect. I uploaded a video:

    Video: https://youtu.be/ZMdPhVEkQ1k

    What do you guys think?
    ???

    Sent from my LG-G710 using Tapatalk

  5. #5
    Join Date
    Oct 2011
    Location
    Gladstone, Oregon (Portland)
    Posts
    1,555
    Post Likes
    That looks like an XV2

  6. #6
    Join Date
    Oct 2018
    Posts
    13
    Post Likes
    Thread Starter
    This is a cooling unit only.

  7. #7
    Join Date
    Oct 2018
    Posts
    13
    Post Likes
    Thread Starter
    XV18

  8. #8
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    24,694
    Post Likes
    Why is it orange?

  9. #9
    Join Date
    Oct 2018
    Posts
    13
    Post Likes
    Thread Starter
    The units have bee painted with Heresite for corrosion protection!

  10. #10
    Join Date
    Nov 2019
    Posts
    2
    Post Likes
    So cooling only unit, with an ERR161.01, your gas temp sensor on the air handler is not reading correctly which is causing the EEV to close. OHM out the sensor and see what it is reading. Run fan only without compressor and compare your resistance reading to return air temp. Should obviously be the same.

  11. #11
    Join Date
    Jan 2004
    Location
    PA
    Posts
    78,070
    Post Likes
    Might want to see what he head pressure is doing.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  12. #12
    Join Date
    Aug 2009
    Location
    Beatrice, NE
    Posts
    9,699
    Post Likes
    If the stat is showing an alert code then the CDA on the air handler should be showing one also.

    I would try to manually open the EEV and see what happens, You can also see what position the EEV is in through the CDA. I would walk through the monitor menu to see what it is reporting.

  13. #13
    Join Date
    Jun 2006
    Location
    Victoria, Texas
    Posts
    621
    Post Likes
    Check the sensor at air handler.