    Quote Originally Posted by HE>I View Post
    Yes sir I crawled in there and sealed everything perfectly!
    Ok good. Did the pressures change at all after? Given the time of year I'd say the return leak was your issue. With the low alarm. What was the sh and sc? Btw hows that pro membership going. You'll get more responses in a locked area of the forum. Maybe ask the mods to hook you up. Idk.

    Sent from my LG-G710 using Tapatalk

  2. #28
    Join Date
    May 2018
    Location
    VA/DC
    Posts
    289
    Post Likes
    You should also take a look at the txv bulbs. Back in the day sporlan had it in the documents, now they don't. But the cap tube coming off the sensing bulb must be at the highest point. If it isnt the txv gets lazy so to say and it will create low pressure situations. Had a 48a that froze up on day one. Set the txv bulbs in the correct position and issue solved.

  3. Likes CEAS-AC-TECH liked this post
  4. #29
    Join Date
    Oct 2015
    Location
    Chino, Ca.
    Posts
    120
    Post Likes
    Thread Starter
    Quote Originally Posted by Cool breeze 38 View Post
    You should also take a look at the txv bulbs. Back in the day sporlan had it in the documents, now they don't. But the cap tube coming off the sensing bulb must be at the highest point. If it isnt the txv gets lazy so to say and it will create low pressure situations. Had a 48a that froze up on day one. Set the txv bulbs in the correct position and issue solved.
    This is good advice! I will take a look.

  5. #30
    Join Date
    Oct 2015
    Location
    Chino, Ca.
    Posts
    120
    Post Likes
    Thread Starter
    Quote Originally Posted by CEAS-AC-TECH View Post
    Ok good. Did the pressures change at all after? Given the time of year I'd say the return leak was your issue. With the low alarm. What was the sh and sc? Btw hows that pro membership going. You'll get more responses in a locked area of the forum. Maybe ask the mods to hook you up. Idk.

    Sent from my LG-G710 using Tapatalk

    They adjusted slightly. I just got a call from the customer saying its doing it again Any ideas?

    Also, still no response. I will submit again

  6. #31
    Join Date
    Oct 2015
    Location
    Chino, Ca.
    Posts
    120
    Post Likes
    Thread Starter
    Quote Originally Posted by buford View Post
    Was it air balanced or proof of correct amount of airflow.

    No sir, it was not air balanced.

  7. #32
    Join Date
    Jul 2011
    Location
    DFW, TX.
    Posts
    1,470
    Post Likes
    Quote Originally Posted by HE>I View Post
    They adjusted slightly. I just got a call from the customer saying its doing it again Any ideas?

    Also, still no response. I will submit again
    You gotta run through the settings and set it up.without that you'll be chasing ghost.

    Sent from my LG-G710 using Tapatalk

  8. #33
    Join Date
    Oct 2015
    Location
    Chino, Ca.
    Posts
    120
    Post Likes
    Thread Starter
    Quote Originally Posted by CEAS-AC-TECH View Post
    You gotta run through the settings and set it up.without that you'll be chasing ghost.

    Sent from my LG-G710 using Tapatalk

    Would you mind if I private messaged or texted you? The tech support isn’t helping at all.

  9. #34
    Join Date
    Jul 2011
    Location
    DFW, TX.
    Posts
    1,470
    Post Likes
    Quote Originally Posted by HE>I View Post
    Would you mind if I private messaged or texted you? The tech support isn’t helping at all.
    Freezin while trying to get off tgis roof atm

    Sent from my LG-G710 using Tapatalk

  10. #35
    Join Date
    Oct 2015
    Location
    Chino, Ca.
    Posts
    120
    Post Likes
    Thread Starter
    Quote Originally Posted by CEAS-AC-TECH View Post
    Freezin while trying to get off tgis roof atm

    Sent from my LG-G710 using Tapatalk
    Yikes! God speed haha

  11. #36
    Join Date
    Jul 2011
    Location
    DFW, TX.
    Posts
    1,470
    Post Likes
    Quote Originally Posted by HE>I View Post
    Yikes! God speed haha
    Thanks. Its an od reznor that wont initiate heat sequence. Got two of these...

    Sent from my LG-G710 using Tapatalk

  12. #37
    Join Date
    May 2018
    Location
    VA/DC
    Posts
    289
    Post Likes
    another thing with ALL rtu units. the factory sized pulley is set for a free flowing concentric ( no static) once you put it on a system with duct work the cfm drops due to static. On every 48 series unit i have put on a 1 inch bigger blower pulley. this about maxed out the amp draw and got the air flow up.

    I installed 3 48A 30 ton units. Before I changed the pulley I had horrible static ( vav system) and I maintained a 52 deg discharge at 100% fan with just two of the 4 compressors. Yeah thats no good. Changed the pulley and much better performance.

    An air balance is always best to make sure youre at the max cfm needed. Also do the math to check max blower wheel rpm.

  13. Likes CEAS-AC-TECH liked this post
  14. #38
    Join Date
    Oct 2015
    Location
    Chino, Ca.
    Posts
    120
    Post Likes
    Thread Starter
    Quote Originally Posted by CEAS-AC-TECH View Post
    Thanks. Its an od reznor that wont initiate heat sequence. Got two of these...

    Sent from my LG-G710 using Tapatalk
    Say a prayer for that old feller and keep it moving haha my first reznor I spent a couple hours chasing a ghost

  15. #39
    Join Date
    Oct 2015
    Location
    Chino, Ca.
    Posts
    120
    Post Likes
    Thread Starter
    Quote Originally Posted by CEAS-AC-TECH View Post
    Thanks. Its an od reznor that wont initiate heat sequence. Got two of these...

    Sent from my LG-G710 using Tapatalk
    Morning! Headed to the job now. Any advice for the start up sequence?