    12" trunkline on 2.5 ton AC...lol.

    I dont usually do new construction but I am going out to help on a rough-in on Saturday to help catch us up. I was looking at the equipment and the associated trunkline sold. 12" main supply trunk and 2.5 ton equipment...lol.

  2. #2
    Join Date
    May 2014
    Location
    Bay Area California
    Posts
    25,378
    Post Likes
    That's not out of the question, provided the trunk isn't wire flex, and the unit is spec'd for higher statics.
    If you were a real tech, you'd solder a relay on that board and call it good to go.

    I do a triple evac with nitro to remove non condensables.

    I use 56% silver on everything except steel.

    Did you really need the " If you were a real tech " ??

  3. #3
    Join Date
    Oct 2011
    Location
    Gladstone, Oregon (Portland)
    Posts
    1,767
    Post Likes
    Thread Starter
    Quote Originally Posted by BBeerme View Post
    That's not out of the question, provided the trunk isn't wire flex, and the unit is spec'd for higher statics.
    Dont have the prints in front of me but I think it is about 20' of 12 then 90s and reduces down to 10 and goes another 15-20'.

    I dont know man....doesnt look right to me. And this isnt high static equipment. Standard .5

  4. #4
    Join Date
    Nov 2006
    Location
    Athens, Ohio
    Posts
    7,177
    Post Likes
    Quote Originally Posted by Adlerberts-Protege View Post
    Dont have the prints in front of me but I think it is about 20' of 12 then 90s and reduces down to 10 and goes another 15-20'.

    I dont know man....doesnt look right to me. And this isnt high static equipment. Standard .5
    So it is the duct system we find in 90% of the houses.
    AOP Rules: Rules For Equipment Owners.

    Free online load calculator: http://www.loadcalc.net/


    There = not here. Their = possessive pronoun. They're = they are
    It's = contraction of it is. Its = the possessive form of it
    Too = also. To = expressing motion. Two = 2
    Then = after that, next. Than = indicates a comparison.
    Questions should end with a question mark "?" Statements end with a period "."

  5. #5
    Join Date
    Oct 2011
    Location
    Gladstone, Oregon (Portland)
    Posts
    1,767
    Post Likes
    Thread Starter
    It is, but we actually have a quality guarantee that the system will be designed within system specs, including proper static. This one worries me.

  6. #6
    Join Date
    Jul 2009
    Location
    South Carolina
    Posts
    6,980
    Post Likes
    There is a common misconception about how much airflow can be achieved under static pressure because TEL of 100 ft. of duct is assumed. 25ft. of a 12" supply can easily handle 1000 CFM's at .1 static but the velocity will be high. It all depends on the rest of the duct system. Manual D compensates for the whole duct system by using the TEL of the longest run & uses the standard of static per 100 ft. of duct. It's an excellent system but it is not perfect.
    I worked some of those numbers out on this ductulator: https://oceanhvac.com/ductulator/
    Gary
    -----------
    http://www.oceanhvac.com
    The best things in life are free but not everyone is willing to pay the price.

  7. Likes CEAS-AC-TECH liked this post
  8. #7
    Join Date
    Oct 2011
    Location
    Gladstone, Oregon (Portland)
    Posts
    1,767
    Post Likes
    Thread Starter
    Quote Originally Posted by garyed View Post
    There is a common misconception about how much airflow can be achieved under static pressure because TEL of 100 ft. of duct is assumed. 25ft. of a 12" supply can easily handle 1000 CFM's at .1 static but the velocity will be high. It all depends on the rest of the duct system. Manual D compensates for the whole duct system by using the TEL of the longest run & uses the standard of static per 100 ft. of duct. It's an excellent system but it is not perfect.
    I worked some of those numbers out on this ductulator: https://oceanhvac.com/ductulator/
    Ya, I used to teach Manual D to a lot of companies when I was in Seattle. I know that our salesman are using Wrightsoft, and that they are supposed to be using it. Highly doubtful on this one.

  9. #8
    Join Date
    Dec 2012
    Location
    columbus, OH
    Posts
    6,951
    Post Likes
    Thats pretty typical on a mobile come. Static pressure will be high no doubt.


    Sent from my iPhone using Tapatalk

  10. #9
    Join Date
    Jan 2004
    Location
    PA
    Posts
    78,337
    Post Likes
    Quote Originally Posted by garyed View Post
    There is a common misconception about how much airflow can be achieved under static pressure because TEL of 100 ft. of duct is assumed. 25ft. of a 12" supply can easily handle 1000 CFM's at .1 static but the velocity will be high. It all depends on the rest of the duct system. Manual D compensates for the whole duct system by using the TEL of the longest run & uses the standard of static per 100 ft. of duct. It's an excellent system but it is not perfect.
    I worked some of those numbers out on this ductulator: https://oceanhvac.com/ductulator/
    20' of 12" with 2-90s. When you include the transition to round at the plenum. Will most likely be close to 100' of TEL.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  11. #10
    Join Date
    Oct 2011
    Location
    Gladstone, Oregon (Portland)
    Posts
    1,767
    Post Likes
    Thread Starter
    Quote Originally Posted by beenthere View Post
    20' of 12" with 2-90s. When you include the transition to round at the plenum. Will most likely be close to 100' of TEL.
    No way is it going to push 1000 cfm.

  12. #11
    Join Date
    Dec 2012
    Location
    columbus, OH
    Posts
    6,951
    Post Likes
    Quote Originally Posted by Adlerberts-Protege View Post
    No way is it going to push 1000 cfm.
    Why not?


    Sent from my iPhone using Tapatalk

  13. #12
    Join Date
    Mar 2015
    Location
    Tx
    Posts
    1,354
    Post Likes
    Quote Originally Posted by Core_d View Post
    Why not?


    Sent from my iPhone using Tapatalk
    Put enough blower in it will
    I don't have a ducalator but IIRC 12" @ .06 or .08 is 700 cfm . It's too darned small unless it's a MH with hi static blower. Run a 10 to a couple of close boots will help

  14. #13
    Join Date
    Dec 2012
    Location
    columbus, OH
    Posts
    6,951
    Post Likes
    Quote Originally Posted by oldguy1949 View Post
    Put enough blower in it will
    I don't have a ducalator but IIRC 12" @ .06 or .08 is 700 cfm . It's too darned small unless it's a MH with hi static blower. Run a 10 to a couple of close boots will help
    Any constant torque motor will put out its design cfm at .9 static or higher with one of the upper speed taps used. Even a psc motor with most systems should do good enough. It happens everyday.


    Sent from my iPhone using Tapatalk