    I was working on a ComfortMaker N8MPN075B12A1 with the Honeywell SV9641M4510 in it.
    I was trying to figure out which wire initiates the heat sequence? I figured it was that "DATA" with but the voltage never changed on it as I cycled the R&W on the board. There are 4 control wires R,C,24VAC & DATA
    Can anyone shed some light on this for me?
    Jun 2017
    Portland, OR(Previous: Arizona, Texas, Oklahoma)
    I feel like this will fall on the pro membership side.
    I'm interested as well and want to know the answer
    Sent from my LM-G710VM using Tapatalk
    Virginia
    Quote Originally Posted by FreeThrowGuy View Post
    You are correct, but we can give general guidance in this forum.
    Virginia
    Quote Originally Posted by ajbeck21 View Post
    What do you mean "voltage never changed"? Did you have voltage or not? If you had voltage, what was it?
    Oct 2010
    Hey rundawg. yes, it had 24volts on it. But like I said it had 24 volts with R&W jumped or not.. it didn't seem like it was the control wire?
    Oct 2010
    I was checking from ground not common though if that would make a difference??
    Virginia
    I want you to google “N8MPN Service Manual 2004 pdf”. When the search results come up, select on “MULTI POSITION SINGLE STAGE 2--STAGE GAS FURNACES”.
    Once you download the manual, go to page 25 to see the voltages for each of the Smart Valve pins.
    These SmartValves are almost always the issue when you have problems with these systems.
    There is your "General Guidance" on this issue.
    Jul 2018
    Wisconsin
    Smart valves were a dumb idea from a paper pusher looking to cheapen up units more than they already are. That being said do you have a flash code?
    Jun 2000
    WYO
    I never could figure out that terminal, still cant for diagnostics. But it's nice to know now what it should be reading. No info about what to do if it's beyond parameters
    Jun 2000
    WYO
    Thanx rundawg for the link
    Oct 2010
    Thanks for that Run...
    So it explains why I was only getting about 17v's or so. I have a bad habit of seeing anything close to 24v & calling it 24.... Lesson learned... AGAIN....
    It still don't really answer the question. Is that the control that will initiate the heating sequence? If it is why did the voltage not changed when I cycled R&W on the board.
    Oct 2010
    The problem was the induce draft blower was FULL of mud divers & wasp. I'm just trying to learn a lil more about this thing..
    Virginia
    As per the electrical page I had you reference in the manual, there is voltage on that "Data" line any time the door interlock switch is closed.
    The Data lines job:
    1. Call for heat signal from board to valve.
    2. Fan "ON" signal from valve back to the board.
    3. Status info on pressure switch, limit switch, ignition state, flame state, ect…