    AAON intermittent flame failures
    The machines are MUA units model: RNA-0-16-C-8-DAAOA-DB3KO.
    There are two spark ignition modules per unit:
    They are Aaon P/N V57870, 1097-850 series direct spark igniter by UTEC.
    When there is a flame failure, diagnostic light flushes 1 time which means “control in one hour lock out”.
    After restarting the machine burners come on all the time. When nothing is done the module resets on its own ( I guess after one hour). I have never seen other faults like:
    2 flushes- Pressure switch open with inducer on
    3 flushes- Pressure switch closed with inducer off
    4 flushes - Limit switch is open
    5 flushes -False flame 1 hour lockout
    Have anyone experienced this situation?
    Dec 2006
    Vancouver, B.C.
    Forgive me for my looking up the numbers...
    Have you checked the flame rod if that is what it is using for flame verification? May be on the cusp of needing replacement or cleaning?
    Also have to checked for proper flame at the burners? Could be a cracked HX, blocked flu or blocked up HX causing the flame to extinguish?
    Quickly, I must hurry, for there go my people and I am their leader!
    montreal
    Corrosion on the ground wire of the Ignition control.
    Ground wire is the one that read the flame signal and get it back to the Ignition control.
    Have you measured uA reading on the flame rod?
    Is the flame rod clean and in good shape?
    Oct 2001
    I think that now I have a pretty good idea what is going on. I believe that flame goes out intermittently because modulating gas valves throttle down to much and either flame is to week to be in contact with flame rod or just simply gets blown away due to low velocity. I wish I had time to watch it and see the flame right before it goes off.
    These intermittent failures were always happening on warmer days. Now when outside temperature dropped, burners fire without issues. I have to reed the manuals and see if lowest opening of valves can be increased.
    edmonds wa
    Checked gas pressure thru all operations?
    UA Local 32 retired as of Jan 2020
    Chicago area
    Does this unit modulate the heat?
    Oct 2001
    Gas pressure wasn't checked through the whole operation and yes, the unit modulate heat.
    There are two stages of heat; two ignition modules, two heat exchangers and two modulating draft inducers.
    First stage has two modulating gas valves and stage two - one modulating valve.
    Nov 2011
    East Side
    have you checked it with a combustion analyzer?
    Oct 2001
    I am in-house maintenance and we don't have combustion analyzer.
    Let's assume that i would have an analyzer and readings were not up to par.
    How one can change the fuel to air ratio in this Aaon? Opening of gas valves and speed of inducer fans is controlled by Modgas controller.
    Jul 2018
    Wisconsin
    I'd assume it's a Maxitrol. If so they are about the easiest valves to adjust. Check your heat exchangers.
    montreal
    Personally I wouldn't do the combustion analysis.
    It's a atmospheric burner and there's not much you can do to adjust combustion.
    Make sure you have the right manifold pressure at high fire.
    Low fire should be around 0.5 in wc
    Oct 2001
    Quote Originally Posted by patpinet View Post
    I believe that this is the best next move. When I get chance I will do that and let you know what readings I had.
    Jul 2018
    Wisconsin
    It has a atmospheric burner???