Thread: AAON intermittent flame failures

  1. #1
    Join Date
    Oct 2001
    Posts
    2,133
    Post Likes

    AAON intermittent flame failures

    The machines are MUA units model: RNA-0-16-C-8-DAAOA-DB3KO.
    There are two spark ignition modules per unit:
    They are Aaon P/N V57870, 1097-850 series direct spark igniter by UTEC.
    When there is a flame failure, diagnostic light flushes 1 time which means “control in one hour lock out”.
    After restarting the machine burners come on all the time. When nothing is done the module resets on its own ( I guess after one hour). I have never seen other faults like:
    2 flushes- Pressure switch open with inducer on
    3 flushes- Pressure switch closed with inducer off
    4 flushes - Limit switch is open
    5 flushes -False flame 1 hour lockout
    Have anyone experienced this situation?

  2. #2
    Join Date
    Dec 2006
    Location
    Vancouver, B.C.
    Posts
    1,731
    Post Likes
    Forgive me for my looking up the numbers...

    Have you checked the flame rod if that is what it is using for flame verification? May be on the cusp of needing replacement or cleaning?

    Also have to checked for proper flame at the burners? Could be a cracked HX, blocked flu or blocked up HX causing the flame to extinguish?


    Sent from my iPhone using Tapatalk
    Quickly, I must hurry, for there go my people and I am their leader!

  3. #3
    Join Date
    Feb 2010
    Location
    montreal
    Posts
    670
    Post Likes
    Corrosion on the ground wire of the Ignition control.
    Ground wire is the one that read the flame signal and get it back to the Ignition control.
    Have you measured uA reading on the flame rod?
    Is the flame rod clean and in good shape?

  4. #4
    Join Date
    Oct 2001
    Posts
    2,133
    Post Likes
    Thread Starter
    I think that now I have a pretty good idea what is going on. I believe that flame goes out intermittently because modulating gas valves throttle down to much and either flame is to week to be in contact with flame rod or just simply gets blown away due to low velocity. I wish I had time to watch it and see the flame right before it goes off.
    These intermittent failures were always happening on warmer days. Now when outside temperature dropped, burners fire without issues. I have to reed the manuals and see if lowest opening of valves can be increased.

  5. #5
    Join Date
    Sep 2007
    Location
    edmonds wa
    Posts
    4,444
    Post Likes
    Checked gas pressure thru all operations?
    UA Local 32 retired as of Jan 2020

  6. #6
    Join Date
    Dec 2004
    Location
    Chicago area
    Posts
    19,137
    Post Likes
    Does this unit modulate the heat?


    Sent from my iPhone using Tapatalk

  7. #7
    Join Date
    Oct 2001
    Posts
    2,133
    Post Likes
    Thread Starter
    Gas pressure wasn't checked through the whole operation and yes, the unit modulate heat.

    There are two stages of heat; two ignition modules, two heat exchangers and two modulating draft inducers.

    First stage has two modulating gas valves and stage two - one modulating valve.

  8. #8
    Join Date
    Nov 2011
    Location
    CO
    Posts
    17,438
    Post Likes
    have you checked it with a combustion analyzer?

  9. #9
    Join Date
    Oct 2001
    Posts
    2,133
    Post Likes
    Thread Starter
    I am in-house maintenance and we don't have combustion analyzer.

    Let's assume that i would have an analyzer and readings were not up to par.

    How one can change the fuel to air ratio in this Aaon? Opening of gas valves and speed of inducer fans is controlled by Modgas controller.

  10. #10
    Join Date
    Jul 2018
    Location
    Wisconsin
    Posts
    1,564
    Post Likes
    I'd assume it's a Maxitrol. If so they are about the easiest valves to adjust. Check your heat exchangers.

    Sent from my SM-G960U using Tapatalk

  11. #11
    Join Date
    Feb 2010
    Location
    montreal
    Posts
    670
    Post Likes
    Personally I wouldn't do the combustion analysis.
    It's a atmospheric burner and there's not much you can do to adjust combustion.

    Make sure you have the right manifold pressure at high fire.
    Low fire should be around 0.5 in wc

  12. #12
    Join Date
    Oct 2001
    Posts
    2,133
    Post Likes
    Thread Starter
    Quote Originally Posted by patpinet View Post
    Personally I wouldn't do the combustion analysis.
    It's a atmospheric burner and there's not much you can do to adjust combustion.

    Make sure you have the right manifold pressure at high fire.
    Low fire should be around 0.5 in wc
    I believe that this is the best next move. When I get chance I will do that and let you know what readings I had.

  13. #13
    Join Date
    Jul 2018
    Location
    Wisconsin
    Posts
    1,564
    Post Likes
    It has a atmospheric burner???

    Sent from my SM-G960U using Tapatalk

  14. #14
    Join Date
    Jul 2009
    Location
    Damascus MD
    Posts
    6,160
    Post Likes
    Quote Originally Posted by patpinet View Post
    Personally I wouldn't do the combustion analysis.
    It's a atmospheric burner and there's not much you can do to adjust combustion.

    Make sure you have the right manifold pressure at high fire.
    Low fire should be around 0.5 in wc
    Dont listen to this guy.

    Perform the combustion analysis.

    There are ways to adjust


    Sent from my iPhone using Tapatalk

  15. Likes thatguy liked this post.
+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •