    Hi all
    I have currently replaced 3 x schnieder alvitar vsd with genuine OEM parts on a French carrier Model 30RBSY120A0002
    Sn M2013030484.of which communicate via the carrier LEN.
    After replacing the drives I have now been advised that I need to perform a attach procedure for the new drives to communicate.
    My question is how I go about carrying out this procedure any information would be greatly appreciated
    Sent from my SM-G965F using Tapatalk
    uk
    Think it's only the Danfoss VSD that requires the attaching procedure.
    Schneider is just plug and play. Just verify the config is similar.
    Gibbo
    Feb 2017
    Australia
    Nope not only danfoss but schnieder drives also require to be attached see below email from Carrier France technical support
    You will have to make the “ATTACH “ Procedure
    You will have just to take care about the unit software when you replace the drive, IT IS MANDATORY TO UPGRADE UNIT SOFTWARE
    BY HIGHER VERSION THAN 3.3
    uk
    Depends on number of circuits if only 1 circuit or 2 circuits if 2 then you will need to attach the drive to the correct circuit you should find this in service configuration. Your software is ok so no issues there.
    Gibbo
    Feb 2017
    Australia
    Looked under service configuration and factory configuration still no luck on this,unless I am overlooking something.
    uk
    Apologies I was looking at a 30 RB,
    Look in Maintenance / DRV_CTRL menu you will see the "attach" at the bottom. It's either set_drv = 1 for A or 2 for B
    All drives should be switched off except the drive you wish to attach.
    Gibbo
    Feb 2017
    Australia
    Thanks Gibbo for your input I will try your steps and keep u posted.
    Feb 2017
    Australia
    Gibbo
    Found how to attach fan vsd as you explained.
    Any ideas on where to attach pump vsd
    uk
    Brett
    Same procedure as you did for fans but now set_drive =3 for variable pump. Remember to switch off fan vsd's while attaching pump vsd.
    Glad to help.
    Gibbo
    Feb 2017
    Australia
    Just cannot work out now where and how to attach chilled water pump vsd.
    Do I also make the chilled water pump circuit a or circuit b fan???
    Feb 2017
    Australia
    Gibbo
    Thanks for your help it is greatly appreciated
    All alarms have cleared now I can test run the chiller
    Thanks again
    uk
    Brett
    No problem glad it all worked out ok.
    Gibbo
    Feb 2017
    Australia
    Gibbo I am testing chiller operation but finding chiller water loop failure due to vsd not running have pump 1 output in status view and drive percentage 93% on touch pilot but vsd not running
    Any tips you might be able to share on this
  14. #14
    Feb 2017
    Australia
    Gibbo
    Also water pump vsd fan failure keeps coming up then reset itself,tried attaching vsd over and over by making it number 3 but no success.
    I also found cond fan vsd not starting or running when using quick test menu on touch pilot.
    Checked all drive settings command mode cond =2 (serial communication)
    frequency mode fnod =4 (serial com ref)
    Any other tips would be of great help
  15. #15
    Feb 2017
    Australia
    Turn mains power off and back on again all vsd faults appear and are unable to reset only way to clear alarms is to re attach the vsd 1 at a time.
    Something weird going on here
  16. #16
    Feb 2017
    Australia
    Gibbo
    If you are able to assist me further on this problem I can send you an email with every procedure carried on VSD as per manual provide by Schneider and findings during works done today.
  17. #17
    uk
    Did you press "Save" after each "Attach" can't think of any other reason at the minute why it didn't retain the settings will have a think over the weekend and get back to you before Monday.
    Gibbo
  18. #18
    Feb 2017
    Australia
    Gibbo
    Email reply sent
    Look forward to your thoughts.
  19. #19
    Feb 2017
    Australia
    Gibbo
    Recently sent u an email of which has returned not delivered have u changed your email ???