    Installed a couple of Honeywell TH6320U2008 thermostats on Rheem heat pumps, both failed within a couple of days, voltage from thermostat to reversing valve varies from 5-23 volts which wont keep valve energized. All other control voltage is dead on 26 volts. All new control wire to both. Have since replaced with some Emerson thermostats and have had no further issues. Just curious if others have seen this issue with any of the T series line.

  2. #2
    Join Date
    Jan 2012
    Location
    Broomall, PA
    Posts
    4,743
    Post Likes
    Did you have the common hooked up? Seems odd that both failed. Did you buy them both at the same time/same place?
    If I do a job in 30 minutes it's because I spent 30 years learning how to do that in 30 minutes. You owe me for the years, not the minutes.

    Helpful Calcs, tips, tricks on my YouTube channel: https://www.youtube.com/channel/UCgm...TUTAdKmqRiTDEg

  3. #3
    Join Date
    Jan 2005
    Posts
    44
    Post Likes
    Thread Starter
    Always have a common. Both were purchased at same time. We buy them 4-6 at a time usually, but usually are using them in straight ac with gas furnace application.

  4. #4
    Join Date
    Sep 2007
    Location
    State College, PA
    Posts
    5,579
    Post Likes
    I have not seen this problem in the dozen or so I have installed. Almost all heat pumps.

    I still prefer the Honeywell 8000 series.
    Can someone please explain to me -
    Why is there never enough time to do it right the first time, but plenty of time to do it twice?


    Please view site rules: http://hvac-talk.com/vbb/showthread.php?t=1241

    Apply for Pro Membership: http://hvac-talk.com/vbb/showthread.php?t=116113

  5. Likes P.Hank, shavedneon, Tom27 liked this post.
  6. #5
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    23,572
    Post Likes
    I sell a shitload of them and rarely have warranty claims
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Why is it that those who complain the most contribute the least?
    MONEY CAN'T BUY HAPPINESS. POVERTY CAN'T BUY ANYTHING

  7. #6
    Join Date
    Jan 2005
    Posts
    44
    Post Likes
    Thread Starter
    1st ones I have had any issues with. Just kinda odd to have 2 in the same house fail the same way. Just thought someone else may have seen a issue similar. I am no a big fan of the stab-lock wire connections, but I know most thermostats are moving that direction.

  8. #7
    Join Date
    Aug 2008
    Location
    Hibbing, MN
    Posts
    1,301
    Post Likes
    I put in tons of these and have not had a problem until last month. New furnace with heat pump. New wiring and T-6 thermostat with 3 heat, 2 cool. Furnace board kept blowing the 3amp fuse. It turned out to be a direct short in the thermostat. Put a different Honeywell statin, and problem solved.
    If God didn't want us to eat animals... He wouldn't have made them out of MEAT.

  9. Likes YOUNG FROSTY liked this post.
  10. #8
    R600a's Avatar
    R600a is offline Professional Member*/Membership Committee
    Join Date
    Jul 2019
    Location
    Hanging out with the mice behind the fridge talking bad about the roaches in the oven.
    Posts
    31,873
    Post Likes
    We sell a ton of the t series and have not had any problems. Our only warranty replacement was a misdiagnosis and the stat was fine.

    Sent from my rotary telephone using Tapatalk
    "Is this before or after you fired the parts cannon at it?" - senior tech
    I'm tired of these mediocre "semi flammable" refrigerants. If we're going to do it let's do it right.
    Unless we change direction we are likely to end up where we are going.
    "It's not new, it's better than new!" Maru.

  11. #9
    Join Date
    May 2018
    Location
    Elizabethtown, PA
    Posts
    181
    Post Likes
    There is a bad batch of T6's. We had five in a row that wouldn't run heat pumps. All our problems were on dual fuel systems but bench testing showed that that wasn't the only issue. Honeywell replaced (upgraded) them through our distributor.

  12. #10
    R600a's Avatar
    R600a is offline Professional Member*/Membership Committee
    Join Date
    Jul 2019
    Location
    Hanging out with the mice behind the fridge talking bad about the roaches in the oven.
    Posts
    31,873
    Post Likes
    I am glad to hear they took good care of you that is the important thing.
    Quote Originally Posted by Rovert View Post
    There is a bad batch of T6's. We had five in a row that wouldn't run heat pumps. All our problems were on dual fuel systems but bench testing showed that that wasn't the only issue. Honeywell replaced (upgraded) them through our distributor.
    Sent from my rotary telephone using Tapatalk
    "Is this before or after you fired the parts cannon at it?" - senior tech
    I'm tired of these mediocre "semi flammable" refrigerants. If we're going to do it let's do it right.
    Unless we change direction we are likely to end up where we are going.
    "It's not new, it's better than new!" Maru.

  13. #11
    Join Date
    Jan 2005
    Posts
    44
    Post Likes
    Thread Starter
    Both of these were duel fuel applications

  14. #12
    Join Date
    Nov 2008
    Location
    Piney Flats, Tn.
    Posts
    2,282
    Post Likes

    th6210u2001

    we had one this week. Installed for 8 days on goodman heat pump. would not bring on the contactor, auxiliary or emergency heat. Fan would run no problem. The voltage would fluctuate between 5v and 20v this did have a common connected.

  15. #13
    Join Date
    Dec 2012
    Location
    columbus, OH
    Posts
    7,049
    Post Likes
    Had my share of bad ones...


    Sent from my iPhone using Tapatalk

  16. #14
    Join Date
    Jul 2018
    Location
    Indiana
    Posts
    44
    Post Likes
    A friend in the trade told me that some of the new honeywell tstats are removing the signal from w or y if there is a short in the wiring. A flooring guy had run a 3" screw into the new tstat wiring and shorted y to common. He thought he had a bad tstat and rep it. when the new one did the same thing (no volt on y) he checked the wiring and found it shorted.

  17. #15
    Join Date
    Jan 2005
    Posts
    44
    Post Likes
    Thread Starter
    I will probably stay away from them for awhile then.

  18. #16
    Join Date
    May 2014
    Location
    Bay Area California
    Posts
    43,457
    Post Likes
    I've installed more than I can remember in commercial applications. Had one fail a day or two later, fan wouldn't come on. Think I had another fail, but can't remember what or why. It's still my normal economical truck stock stat.
    I do a triple evac with nitro to remove non condensables.

  19. #17
    R600a's Avatar
    R600a is offline Professional Member*/Membership Committee
    Join Date
    Jul 2019
    Location
    Hanging out with the mice behind the fridge talking bad about the roaches in the oven.
    Posts
    31,873
    Post Likes
    Same here you get a bad one every once in a while of almost anything.

    Sent from my rotary telephone using Tapatalk
    "Is this before or after you fired the parts cannon at it?" - senior tech
    I'm tired of these mediocre "semi flammable" refrigerants. If we're going to do it let's do it right.
    Unless we change direction we are likely to end up where we are going.
    "It's not new, it's better than new!" Maru.

  20. #18
    Join Date
    May 2016
    Location
    Montreal,canada
    Posts
    24
    Post Likes
    I had 2 fail on me within 6 months of installation: First one thermostat button were unresponsive to anything and after removing thermostat and battery for one week, put back the battery and seem to work but did replace since i dont trust it. Second one after big wind and lot of power surge thermostat lost ALL config and went back to default config.

  21. #19
    Join Date
    Apr 2006
    Location
    Houston, Texas
    Posts
    49
    Post Likes
    Thanks for the info . We use them on all of our heat pump installs. Will keep a look out for problems, but, none so far

  22. #20
    Join Date
    Aug 2009
    Location
    Rhode Island
    Posts
    51
    Post Likes
    we have also had to replace a fair amount of t6

+ Reply to Thread
Page 1 of 16 1234567811 ... LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •