    Honeywell TR-71

    What is the cable and software needed to connect to a syder controller though a TR-71 TSTAT?

  2. #2
    Join Date
    Jun 2018
    Location
    Bay saint louis ms
    Posts
    74
    Post Likes
    It’s been replaced another super expensive part


    Sent from my iPhone using Tapatalk

  3. #3
    Join Date
    May 2004
    Location
    SE Pennsylvania
    Posts
    1,910
    Post Likes
    Ax workbench licensed, running correct version of spyder tool, having original program file, lon adapter or rs485 adapter depending on if the controller is Lon or Bacnet and if someone ran a network wire to the tr71 for the lon port. The sbus is a proprietary network for devices only. If the spyder is networked to a Jace it can be accessed from there. Best bet is to call their controls vendor.