    Mixing of oils.

    So I have began to do a small amount of research on oils mixing. From what I can gather, at first this was thought that even very small amounts of oil mixing would cause sludge, breakdown, etc. But more recent information from some sources states that slight mixing/contamination of oils is not really an issue. For instance using the same gauge set for poe and pve. Yes poe undergoes hydrolisys a pve does not, but as far as I understand it, the oils themselves do not react in any adverse way to coming in contact with each other. Why then do most manufactures still say not to allow any Cross-contamination at all? My understand that good purging practices with your manifold would be enough and I haven't really seen evidence that using separate gauges and hoses for different oils is necessary. Having a separating hose set for burnouts/dirty systems seems more important than different oils.

  2. #2
    Join Date
    Mar 2015
    Location
    Medford, N.Y.
    Posts
    10,203
    Post Likes
    What sources? I remember the original rule of 95% poe vs 5% mineral.

    A seperate set of gauges for burnouts?? Please explain? I use F/D in line on burnouts.

  3. #3
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    8,082
    Post Likes
    The issue of “mixing oils” has nothing to do with the oil. It has to do with converting from one refrigerant to another when the new refrigerant requires a different oil. The concern is if there is too much of the previous oil in the system, the oil may not travel through the lines properly and return to the compressor in a timely manner. Sure, there could be a chemical compatibility issue between the different types or brands of oils, but we really haven’t seen that issue.
    "Right" is not the same as "Wise".

    Don't step on my favorite part of the Constitution just to point out your favorite part.

    Just because you can measure it, doesn't mean it is important. Just because you can't measure it, doesn't mean it isn't important.

  4. #4
    Join Date
    Mar 2018
    Location
    Chesapeake, VA
    Posts
    17
    Post Likes
    Thread Starter
    It seems to me that rather than the manufacturers (I am currently going through some manufacturers training) placing an emphasis on never ever mixing oil (they recommend completely separate gauges for ea H type of oil) it would make more sense to emphasize making sure contaminates from a burnout or known system that was contaminated.

  5. #5
    Join Date
    Mar 2018
    Location
    Chesapeake, VA
    Posts
    17
    Post Likes
    Thread Starter
    I know that mineral oil is not miscible with 410a. Doesn't mean one tiny drop of mineral oil would hurt a system. What I am really focusing on is is that a manufacturer stating that you cannot use gauges for poe and pve. I just haven't seen any evidence that it would actually cause an issue. 1 if purging your gauges thd amount of oil left woulc be extremely small and 2 they are both miscible with 410 the biggest difference is one breaks down in the prescense of moisture the other absorbs it but doesn't turn into acid

  6. #6
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    23,575
    Post Likes
    I'm pretty sure I have read somewhere that 10%-15% is acceptable.

    As far as the paranoia....don't worry about it. Refrigeration techs have been dealing with different refrigerants and oils since 1995 when 12 was outlawed. There have been a few hurdles here and there, but it's not as bad as you think.
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Why is it that those who complain the most contribute the least?
    MONEY CAN'T BUY HAPPINESS. POVERTY CAN'T BUY ANYTHING

  7. #7
    Join Date
    Mar 2015
    Location
    Medford, N.Y.
    Posts
    10,203
    Post Likes
    Well at my last Copeland COSS thing, we were notified that a 50% poe/50% mineral oil is now "OK". A set of hoses for each oil? Mineral,Alke-Benzene,POE,PVE.?

  8. #8
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    23,575
    Post Likes
    Quote Originally Posted by TechmanTerry View Post
    Well at my last Copeland COSS thing, we were notified that a 50% poe/50% mineral oil is now "OK". A set of hoses for each oil? Mineral,Alke-Benzene,POE,PVE.?
    Need 2 sets of hoses. One for systems with dye, and one for systems without dye....I hate dye
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Why is it that those who complain the most contribute the least?
    MONEY CAN'T BUY HAPPINESS. POVERTY CAN'T BUY ANYTHING

  9. #9
    Join Date
    Dec 2014
    Posts
    3,941
    Post Likes
    Just did an 06E from 22 to 407C.
    Carlisle wants 30% POE.
    RTU 50ton. Theres only mineral oil in there right now. Returning like a champ. But, I disabled it now till next spring. Want to watch it run unloaded for a while.

    Sent from my SM-G950U using Tapatalk

  10. #10
    R600a's Avatar
    R600a is offline Professional Member*/Membership Committee
    Join Date
    Jul 2019
    Location
    Hanging out with the mice behind the fridge talking bad about the roaches in the oven.
    Posts
    31,873
    Post Likes
    My understanding is that pag doesn't mix with mineral oil but all others mix any way you like.
    The only problem is when you have mineral oil and it has some moisture from improper installation and service techniques and you add poe to it then you have a problem.

    Sent from my rotary telephone using Tapatalk
    "Is this before or after you fired the parts cannon at it?" - senior tech
    I'm tired of these mediocre "semi flammable" refrigerants. If we're going to do it let's do it right.
    Unless we change direction we are likely to end up where we are going.
    "It's not new, it's better than new!" Maru.

  11. #11
    Join Date
    Mar 2018
    Location
    Chesapeake, VA
    Posts
    17
    Post Likes
    Thread Starter
    Thanks guys. Why are certain manufacturers still stating such strict policies? CYA essentially?

  12. #12
    Join Date
    Nov 2011
    Location
    CO
    Posts
    17,439
    Post Likes
    Quote Originally Posted by stephen90 View Post
    Thanks guys. Why are certain manufacturers still stating such strict policies? CYA essentially?

    a manufacturer is always going to state never to mix oils, never use generic parts, etc. etc. they are protecting their equipment (and their butts). If they, even once say (officially) that it's ok to mix oils, then someone has a compressor failure within the warranty period, they would be responsible for the coverage.

    If someone has a compressor failure within the warranty period, and the manufacturer finds that they have mixed oils, there is no coverage.


    I use the same manifold and gauge set on everything. If I think I may have picked up some contaminates, I'll just blow everything out with nitrogen. If you want to get extreme, use some lineset flush.

    As was stated, mixing oils isn't as big of an issue as was originally thought. manufacturers are coming around apparently, evidenced by Terry saying copeland is now officially stating a 50/50 mix is OK. last class I went through with them, it was unofficial. Nothing is official with any manufacturer unless they put it in a publicly released document addressing the issue, though.

  13. Likes icy78 liked this post.
  14. #13
    Join Date
    Jul 2000
    Location
    Guayaquil, EC
    Posts
    14,652
    Post Likes
    Quote Originally Posted by stephen90 View Post
    So I have began to do a small amount of research on oils mixing. From what I can gather, at first this was thought that even very small amounts of oil mixing would cause sludge, breakdown, etc. But more recent information from some sources states that slight mixing/contamination of oils is not really an issue. For instance using the same gauge set for poe and pve. Yes poe undergoes hydrolisys a pve does not, but as far as I understand it, the oils themselves do not react in any adverse way to coming in contact with each other. Why then do most manufactures still say not to allow any Cross-contamination at all? My understand that good purging practices with your manifold would be enough and I haven't really seen evidence that using separate gauges and hoses for different oils is necessary. Having a separating hose set for burnouts/dirty systems seems more important than different oils.
    It's true that back in the early days a POE oil being used in HVACR there was a strict warning from OEMs to use a dedicated manifold gauge set for POE systems. This rule, along with the one for 5% max residual mineral oil, gradually were disproved...unofficially. Now after more then 25 years the separate gauge set mandate has essentially disappeared and there seems to be some cracks in the OEM's 5% mineral oil edict.

  15. #14
    Join Date
    May 2004
    Location
    SE Pennsylvania
    Posts
    2,617
    Post Likes
    Quote Originally Posted by 2sac View Post
    Need 2 sets of hoses. One for systems with dye, and one for systems without dye....I hate dye
    Yeah the second set are the guys set who put the dye in.

  16. #15
    Join Date
    Jun 2012
    Location
    Northern NV
    Posts
    3,404
    Post Likes
    I have one set of gauges just for 134a systems. 134a and cap tubes are a pita so I do not want any chance of cross contamination. One set of gauges for all the others...

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •