    Air handler vibrating when heat pump in heat mode

    Had a customer call me about a Trane AH causing heavy vibration when the heat comes on, when the unit is in cool mode it all works well with no vibration.. I ran the heat pump in cool mode and disconnected the orange reverse valve outside and immediately it starts to vibrate at the air handler. Im thinking replace TXV with check valve still under wareanty. Both indoor and outdoor coils were clean as well as air filter and blower wheel

    Trane AH
    M#GAF2A0A30S21SAA
    S#121415TD2V

    TrAne HP
    M#4TWB3030C1000AA
    S#12174M9N4F

    OD temp 64F
    R410
    Suction 130 psi
    Liquid 400 psi
    Compressor max amps rated 11.5 actual 7.8
    OD fan max amps rated .74 actual .7
    Capacitor was rated 40/5uf and tested the same

    Indoor was 70F
    Blower motor max rated 1.7 actual 1.4

  2. #2
    Join Date
    Jan 2012
    Location
    Missouri, USA
    Posts
    1,504
    Post Likes
    What was sh/sc in heat mode?

  3. #3
    Join Date
    Jan 2013
    Posts
    67
    Post Likes
    Thread Starter
    I didnt take SH or SC..I also spoke to Trane tech support and he also told me that he would suggest replacing the Outdoor TXV and filter drier

  4. #4
    Join Date
    Dec 2019
    Location
    Jacksonville, Fl
    Posts
    6
    Post Likes
    Ive had a changeover valve not complete its travel and create a hammering type noise/vibration. Did your pressures bounce around at all? Amperage at O on valve coil wire? I had to dig a set of analog gauges out to catch it.

  5. #5
    Join Date
    Jan 2013
    Posts
    67
    Post Likes
    Thread Starter
    I finally found the issue..homeowner had a different company replace the compressor and they never put back the rubber mount legs and the idiot thought that the muffler was a filter drier and removed it and added a second filter drier

  6. #6
    Join Date
    May 2006
    Posts
    3,656
    Post Likes
    I would have had the homeowner call them with you present and have them come fix the problem they created

  7. #7
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    6,661
    Post Likes
    Quote Originally Posted by pctech View Post
    I would have had the homeowner call them with you present and have them come fix the problem they created
    JosA and JosB ....

  8. #8
    Join Date
    Dec 2019
    Location
    westchester ny
    Posts
    33
    Post Likes
    I'm curious why the rubber mounts were only a problem in heating mode

  9. #9
    Join Date
    Jan 2013
    Posts
    67
    Post Likes
    Thread Starter
    This is a base model Trane heat pump they kinda make noise during heat mode, the amps increase during winter time causing the motor on the compressor to vibrate and produce noise especially refrigerant pulsing thru discharge line

  10. #10
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    25,680
    Post Likes
    So how does the amperage increase in heat mode?

  11. #11
    Join Date
    Jan 2013
    Posts
    67
    Post Likes
    Thread Starter
    Same way a dirty condenser increases head pressure,amps and compressor becomes noisy..remember theres a filter inside when the evap becomes the condenser plus its warmer when heat is on during winter season. Ive always noticed that during my check ups on most systems when checking outdoor unit

  12. #12
    Join Date
    Feb 2006
    Location
    Float'N Vally, MS
    Posts
    2,832
    Post Likes
    Quote Originally Posted by Ac_man View Post
    Same way a dirty condenser increases head pressure,amps and compressor becomes noisy..remember there’s a filter inside when the evap becomes the condenser plus it’s warmer when heat is on during winter season. I’ve always noticed that during my check ups on most systems when checking outdoor unit
    I don't know about all this.....

    the idiot thought that the muffler was a filter drier and removed it and added a second filter drier
    But on Trane, this will cause pulsations/vibrations for sure...
    Life is too short, Behappy!
    TFMM

  13. #13
    Join Date
    Apr 2006
    Location
    Tyler, Tx
    Posts
    1,248
    Post Likes
    I thought the vibration was at the Air Handler?
    Philippians 4:13
    I can do all things in him that strengthen me.
    Apostle Paul inspired by GOD.