    Trane XL16 Heatpump problem

    2010 5 ton xl16 heatpump model #4TWX6060E1000AA that is short cycling in heating mode, kicking out on high pressure. Cooling mode cools perfect but has a high subcool at 20 superheat at 3 degrees. Have tested out eev board and everything seems to be operating correctly. Scratching my head on this one, I dont normally work on many trane units unless its changing them out for something else. Any input or suggestions would be greatly appreciated.

  2. #2
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    14,048
    Post Likes
    Take SC at indoor unit

    Sounds like not enough air moving

  3. #3
    Join Date
    Jan 2012
    Location
    Missouri, USA
    Posts
    3,963
    Post Likes
    Verify indoor airflow, was the 20 sc in cool mode? Sounds overcharged.

  4. #4
    Join Date
    Oct 2019
    Location
    Yoakum, TX
    Posts
    11
    Post Likes
    Thread Starter
    Quote Originally Posted by ksefan View Post
    Verify indoor airflow, was the 20 sc in cool mode? Sounds overcharged.
    Was overcharged, and no expansion valve in new goodman air handler. Company that installed indoor unit got it running to cool and didnt worry about heating.

  5. #5
    Join Date
    Jan 2012
    Location
    Missouri, USA
    Posts
    3,963
    Post Likes
    Probably had a leak in the expensive Trane evaporator, now they got a pos Frankenstein. Still better that a Goodman matched system.

  6. #6
    Join Date
    Dec 2007
    Posts
    13,231
    Post Likes
    Provide numbers that would help us help you.
    Indoor temp
    Outdoor temp
    Airflow
    Metering devices(you say no indoor expansion valve, so piston inside?)
    Mode of operation numbers were taken in
    Indoor unit info
    Indoor coil info

    Is it wired correctly? Trane has some different wiring compared to most mfrs.
    The Food Stamp Program, administered by the U.S. Department of Agriculture, is proud to be distributing the greatest amount of free meals and stamps EVER.
    Meanwhile, the National Park Service, administered by the U.S. Department of the Interior, asks us to "Please Do Not Feed the Animals". Their stated reason for this policy "... the animals become dependent on handouts and will not learn to take care of themselves."
    from an excerpt by Paul Jacob in Sun City, AZ

  7. #7
    Join Date
    Dec 2002
    Location
    in a house, Appomattox, Va.
    Posts
    5,598
    Post Likes
    mismatched system is crap shoot. first sounds like overcharge in cooling, 16i usually ran 6-12 sc and 15-18 sh.

    have seen mismatched systems where there is no winning on charge, not enough to cool gets heat. enough to cool kicks psi switch in heat.
    Col 3:23


    questions asked, answers received, ignorance abated

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •