    Carrier RTU Question

    I am going to look at a Carrier 48TCED14A3A5-0A0A0 tomorrow. The issue is apparently the compressor is coming on and going off on high pressure continuously but no outdoor or indoor fan is coming on a cooling call. I haven't looked at it yet so I was hoping that someone here may have ran into this issue on this particular unit and could tell me a couple of things to look for before I climb up there. I find it kind of weird that both indoor and outdoor fans aren't coming on. Thanks!

  2. #2
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    7,931
    Post Likes
    Might be 2 different issues. Not much to those units. If I had to go out on a limb, I'd bet you have issues with overheated/melted wiring
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Liberalism-Ideas so good they mandate them

  3. #3
    Join Date
    Mar 2010
    Location
    Arnold, Mo
    Posts
    955
    Post Likes
    Thread Starter
    Quote Originally Posted by 2sac View Post
    Might be 2 different issues. Not much to those units. If I had to go out on a limb, I'd bet you have issues with overheated/melted wiring
    I didn't think there's much to it. I mostly see Yorks around here.

  4. #4
    Join Date
    Jul 2018
    Location
    Wisconsin
    Posts
    974
    Post Likes
    Check your thermostat.

    Sent from my SM-G960U using Tapatalk

  5. #5
    Join Date
    Mar 2010
    Location
    Arnold, Mo
    Posts
    955
    Post Likes
    Thread Starter
    Quote Originally Posted by Spitz View Post
    Check your thermostat.

    Sent from my SM-G960U using Tapatalk
    I'll check it.

  6. #6
    Join Date
    Jul 2018
    Location
    Wisconsin
    Posts
    974
    Post Likes
    Not sure about the new units but the older ones if y2 was energized on the board the compressor would start. No indoor fan no condenser fans. Y1 would start the condenser fans. Indoor fans wont run without g energized.

    Sent from my SM-G960U using Tapatalk

  7. Likes bigboi0523 liked this post
  8. #7
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    31,426
    Post Likes
    Quote Originally Posted by flanders View Post
    The issue is apparently the compressor is coming on and going off on high pressure continuously but no outdoor or indoor fan is coming on a cooling call.
    Let's assume that this is a no cooling call.

    How do you know the information stated above? Was there another tech from your co? A building maintenance guy?

    I am never handed info like that before I go to a call, so I am curious about the dynamic.....
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  9. #8
    Join Date
    Mar 2010
    Location
    Arnold, Mo
    Posts
    955
    Post Likes
    Thread Starter
    Quote Originally Posted by timebuilder View Post
    Let's assume that this is a no cooling call.

    How do you know the information stated above? Was there another tech from your co? A building maintenance guy?

    I am never handed info like that before I go to a call, so I am curious about the dynamic.....
    Son/ apprentice got his eyes (not hands) on it 1st.

  10. #9
    Join Date
    Jan 2010
    Posts
    17,315
    Post Likes
    Jump it out at the unit and see what gives

  11. #10
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    31,426
    Post Likes
    Three days later...an update?
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  12. #11
    Join Date
    Mar 2010
    Location
    Arnold, Mo
    Posts
    955
    Post Likes
    Thread Starter
    Quote Originally Posted by timebuilder View Post
    Three days later...an update?
    Went back the next day and it was running fine. I'm not sure what was going on but as of now it's operating normally.

  13. #12
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    31,426
    Post Likes
    If there is a smoke detector connected to the board SD terminals, that's your answer.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  14. #13
    Join Date
    Mar 2010
    Location
    Arnold, Mo
    Posts
    955
    Post Likes
    Thread Starter
    Quote Originally Posted by timebuilder View Post
    If there is a smoke detector connected to the board SD terminals, that's your answer.
    Thanks for the info. I'll check it next time I'm out there.