    I have a unit that until last week was running fine. Suddenly started tripping AC undervoltage.
    I pulled the diagnostic history and found that the volts and amps were not recorded at shutdown.It starts and runs for about 20 seconds and trips out. I press the sss motor current/volts button and it says that the solid state starter is not installed. Has anyone ran into this before.
    Jan 2013
    United Kingdom
    Is the Optiview configured for SSS type starter , are comms established between Optiview and SSS trigger board ? Is overload setting correct in Optiview motor display ? Do you see any data in SSS on Optiview display or is it all XXX’s
    Indiana
    It is a Millinium single line panel. Does not seem to be communicating with the SSS. Don’t see the unit voltage or amperage. Does not show what the FLA set point is under %current limit where it normally does.
    Indiana
    It appears that the small ribbon cable was not making good connection between J6 on the logic board and J2 on the micro board.
    Jan 2013
    United Kingdom
    Why do people still have millennium panels ? I hope all working ok now
    Jun 2010
    U.A. (upper Alabama)
    Quote Originally Posted by always looking View Post
    Yep! That bit me on the a$$ one time.
    Nov 2011
    East Side
    Quote Originally Posted by raptyr View Post
    Cause it’s hard to sell a customer on a $20,000 upgrade when the existing panel is working fine.
    Indiana
    Quote Originally Posted by 71CHOPS View Post
    Correct, this location has a 1958 Trane bench grinder with the original panel and hasn’t been overhauled for over 30 years.