    Quote Originally Posted by timebuilder View Post
    When I have a York with a crossover tube ignition, I write it up to rebuild the entire section. I replace the gas valve, all the crossover tubing, and the orifice. I clean the burners and I replace the ignition module.
    It is not worth it to try and dig through this step by step, because it is such a unreliable design.
    If the unit is more than 10 years old, I replace the rollout switch and both the primary and secondary safety switches as well.
    Ditto
    Local 449?
    Aug 2015
    Buffalo,NY
    All you need is a wire brush and some nitro to clean it. Takes longer to pull it out then it dose to clean.
    Southeastern Pa
    I think I have recycled 25 lbs of aluminum from those gas valves alone.
    If they want it to work now, I would rebuild it. Anything less and you could get dinged by return visits. And those rollouts are notorious!
    2 Tim 3:16-17
    Member, IAEI
    AOP Forum Rules:
  4. Likes Metalman0880 liked this post.
  5. #17
    Aug 2015
    Buffalo,NY
    Blue box of death. Those ignition controls suck.
  6. Likes heatingman, BALloyd liked this post.
  7. #18
    Jan 2010
    Quote Originally Posted by Metalman0880 View Post
    Three strikes it's out.
  8. #19
    Southeastern Pa
    Question:
    How can you tell if a JCI ignition module is bad...?
    Name:  How can you tell...JPG
    2 Tim 3:16-17
    Member, IAEI
    AOP Forum Rules:
  9. Likes Metalman0880, heatingman liked this post.
  10. #20
    Quote Originally Posted by heatingman View Post
    At the very least, the entire burner rack needs to be removed for cleaning.
    Manuals will not help with the task.
    I typically use the same approach as Timebuilder.
    In fact I think its a universal standard procedure for those that have worked on York units with any frequency.
    However, the oriface I typically keep, they dont go bad.
    Also, how on earth do you know the gas to the pilot is adequate?
    Never said gas to the pilot is adequate, gas on pilot outlet ov the valve has good pressure. Checked with manometer.
  11. #21
    Chicago area
    Thats what I was getting at, pressure does not equal volume.
  12. #22
    Went back, took apart burner assembly, replaced part of pilot tube, cleaned orifice and holes on crossover tube. For some reason couldn’t get old orifice out. It’s running. I also replaced spark rod and flame sensor. Don’t want to go back for stupid calls. Thanks for all inputs.
  13. Likes Metalman0880 liked this post.
  14. #23
    Southeastern Pa
    That's good.
    The orifice is held in by a crimp on the crossover tube into a groove in the circumference of the orifice.
    Get that Lisle tool for future tests. It can be impossible to hear a spark on a windy roof, and it takes place on the other side of that metal wall. If you have the tool, you can easily confirm a spark.