    Quote Originally Posted by timebuilder View Post
    When I have a York with a crossover tube ignition, I write it up to rebuild the entire section. I replace the gas valve, all the crossover tubing, and the orifice. I clean the burners and I replace the ignition module.

    It is not worth it to try and dig through this step by step, because it is such a unreliable design.

    If the unit is more than 10 years old, I replace the rollout switch and both the primary and secondary safety switches as well.
    Ditto
    Local 449?

  2. #15
    Join Date
    Aug 2015
    Location
    Buffalo,NY
    Posts
    1,017
    Post Likes
    All you need is a wire brush and some nitro to clean it. Takes longer to pull it out then it dose to clean.


    Sent from my iPhone using Tapatalk

  3. #16
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,120
    Post Likes
    I think I have recycled 25 lbs of aluminum from those gas valves alone.

    If they want it to work now, I would rebuild it. Anything less and you could get dinged by return visits. And those rollouts are notorious!
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  4. Likes Metalman0880 liked this post.
  5. #17
    Join Date
    Aug 2015
    Location
    Buffalo,NY
    Posts
    1,017
    Post Likes
    Quote Originally Posted by timebuilder View Post
    I think I have recycled 25 lbs of aluminum from those gas valves alone.

    If they want it to work now, I would rebuild it. Anything less and you could get dinged by return visits. And those rollouts are notorious!
    Blue box of death. Those ignition controls suck.


    Sent from my iPhone using Tapatalk

  6. Likes heatingman, BALloyd liked this post.
  7. #18
    Join Date
    Jan 2010
    Posts
    18,673
    Post Likes
    Quote Originally Posted by Metalman0880 View Post
    Blue box of death. Those ignition controls suck.


    Sent from my iPhone using Tapatalk
    Three strikes it's out.

  8. #19
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,120
    Post Likes
    Question:

    How can you tell if a JCI ignition module is bad...?


    Name:  How can you tell...JPG
Views: 74
Size:  109.9 KB
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  9. Likes Metalman0880, heatingman liked this post.
  10. #20
    Join Date
    Mar 2005
    Posts
    284
    Post Likes
    Thread Starter
    Quote Originally Posted by heatingman View Post
    At the very least, the entire burner rack needs to be removed for cleaning.

    Manuals will not help with the task.

    I typically use the same approach as Timebuilder.

    In fact I think its a universal standard procedure for those that have worked on York units with any frequency.

    However, the oriface I typically keep, they dont go bad.

    Also, how on earth do you know the gas to the pilot is adequate?




    Sent from my iPhone using Tapatalk
    Never said gas to the pilot is adequate, gas on pilot outlet ov the valve has good pressure. Checked with manometer.


    Sent from my iPhone using Tapatalk

  11. #21
    Join Date
    Dec 2004
    Location
    Chicago area
    Posts
    8,746
    Post Likes
    Thats what I was getting at, pressure does not equal volume.




    Sent from my iPhone using Tapatalk

  12. #22
    Join Date
    Mar 2005
    Posts
    284
    Post Likes
    Thread Starter
    Went back, took apart burner assembly, replaced part of pilot tube, cleaned orifice and holes on crossover tube. For some reason couldn’t get old orifice out. It’s running. I also replaced spark rod and flame sensor. Don’t want to go back for stupid calls. Thanks for all inputs.


    Sent from my iPhone using Tapatalk

  13. Likes Metalman0880 liked this post.
  14. #23
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,120
    Post Likes
    That's good.

    The orifice is held in by a crimp on the crossover tube into a groove in the circumference of the orifice.

    Get that Lisle tool for future tests. It can be impossible to hear a spark on a windy roof, and it takes place on the other side of that metal wall. If you have the tool, you can easily confirm a spark.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  15. Likes Metalman0880 liked this post.
Page 2 of 2 FirstFirst 12

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •