    Saturation temperature

    Iam a fooooooollllllll.....???
    What saturation temperature should i maintain on different types of systems ?
    In case of an air conditioner ,
    4.4C is the saturated suction temp.
    So we maintaining the suction pressure to get the proper saturation temp.
    ie R22 68.5 psig = 4.4C
    R134a 35 psig = 4.4
    R 410a 118 = 4.4

    What saturation temperature need for walk in freezer ? (-21C room temp)

    What saturation temperature need for walk in chiller ? (3C room temp )
    If you give the saturation temp. I can calculate suction pressure of different refrigerants .

  2. #2
    Join Date
    Oct 2016
    Location
    Clearwater, Florida
    Posts
    1,443
    Post Likes
    Do yourself a favor and post in *F it's what 90% of the users here use, most probably don't want to have to sit and covert it over to answer your question.

  3. #3
    Join Date
    Mar 2018
    Location
    United Arab Emirates
    Posts
    15
    Post Likes
    Thread Starter
    It's not a joke, i am totally confused because first time in refrigeration

  4. #4
    Join Date
    Oct 2016
    Location
    Clearwater, Florida
    Posts
    1,443
    Post Likes
    I'm sure its not a joke.

    I can help you, just translate your *C readings into *F and I'll help you.

  5. #5
    Join Date
    Mar 2018
    Location
    United Arab Emirates
    Posts
    15
    Post Likes
    Thread Starter
    What saturation temperature should i maintain on different types of systems ?
    In case of an air conditioner ,
    40F is the saturated suction temp.
    So we maintaining the suction pressure to get the proper saturation temp.
    ie R22 68.5 psig = 40F
    R134a 35 psig = 40F
    R 410a 118 = 40F

    What saturation temperature need for walk in freezer ? (-6F room temp needed)

    What saturation temperature need for walk in chiller ? (36F room temp needed)
    If you give the saturation temp. I can calculate suction pressure of different refrigerants .

  6. #6
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    24,331
    Post Likes
    Quote Originally Posted by faisalfadak View Post
    What saturation temperature should i maintain on different types of systems ?
    In case of an air conditioner ,
    40F is the saturated suction temp.
    So we maintaining the suction pressure to get the proper saturation temp.
    ie R22 68.5 psig = 40F
    R134a 35 psig = 40F
    R 410a 118 = 40F

    What saturation temperature need for walk in freezer ? (-6F room temp needed)

    What saturation temperature need for walk in chiller ? (36F room temp needed)
    If you give the saturation temp. I can calculate suction pressure of different refrigerants .
    The metering device and air flow determine that!

  7. #7
    Join Date
    Oct 2016
    Location
    Clearwater, Florida
    Posts
    1,443
    Post Likes
    So on walk in units, you aim for about 10-15*F lower than the box temp.

    So if you want the room temp to be 36*F then look at your P/T chart and find what the refrigerant is 10-15*F below that.

    Freezers are about the same, maybe 20*F less than the box temp.

    Does that make sense or you need more info?