Results 14 to 21 of 21
    Southold, NY
    Quote Originally Posted by ARIOSTO1 View Post
    Ok you should have 65 psi or more in your suction line reading for r22
    Once you are sure your airflow is good
    That involve
    Proper ductwork
    Clean evaporator
    Blower wheel clean
    Blower motor rpm and capacitor
    Clean filter
    Try adding r22
    If no changes.... you have a refrigerant restriction
    Did you installed liquid or suction line filters
    Pressures without temperatures are worthless!
    Oct 2019
    New air filter installed
    air flow is good
    condenser clean
    installed new liquid line filter
    if liquid line blocked condenser pressure is not rising it is 200 psi so less chance
    I will add more gas let me see , i will post the rsult
    Apr 2003
    St. Louis
    Is the expansion device a orfice if so check the number.
    have you looked at the indoor coil to make sure its clean ? Shine a light into the coil fins and loook deep
    Southold, NY
    Quote Originally Posted by gilbert450 View Post
    air flow is good
    condenser clean
    Air flow is fine is not a measurement.
    Liquid line blocked, how?
    Adding more gas? Guessing.
    You need measurements not guessing.
    Super heat
    Sub cooling
    Static pressure.
    The SH and SC values you posted sound like you didn’t check them and are just giving a guesstimate range.
    Please take actual pressure and temp readings of the lines along with indoor and outdoor temps st the time you take the other readings.
    Check your airflow, also was it charged with new R-22 or something else?
    Dec 2019
    Jacksonville, Fl
    Did you pull a deep vacuum after installing compressor? How many microns?