    Quote Originally Posted by ARIOSTO1 View Post
    Ok you should have 65 psi or more in your suction line reading for r22
    Once you are sure your airflow is good
    That involve
    Proper ductwork
    Clean evaporator
    Blower wheel clean
    Blower motor rpm and capacitor
    Clean filter
    Try adding r22
    If no changes.... you have a refrigerant restriction
    Did you installed liquid or suction line filters


    Sent from my iPhone using Tapatalk
    Pressures without temperatures are worthless!

  2. #15
    Join Date
    Oct 2019
    Posts
    4
    Post Likes
    Thread Starter
    New air filter installed
    air flow is good
    condenser clean
    installed new liquid line filter
    if liquid line blocked condenser pressure is not rising it is 200 psi so less chance
    I will add more gas let me see , i will post the rsult

  3. #16
    Join Date
    Apr 2003
    Location
    St. Louis
    Posts
    1,269
    Post Likes
    Is the expansion device a orfice if so check the number.

  4. #17
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    6,656
    Post Likes
    have you looked at the indoor coil to make sure its clean ? Shine a light into the coil fins and loook deep

  5. #18
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    25,622
    Post Likes
    Quote Originally Posted by gilbert450 View Post
    New air filter installed
    air flow is good
    condenser clean
    installed new liquid line filter
    if liquid line blocked condenser pressure is not rising it is 200 psi so less chance
    I will add more gas let me see , i will post the rsult
    Air flow is fine is not a measurement.
    Liquid line blocked, how?
    Adding more gas? Guessing.

    You need measurements not guessing.
    Super heat
    Sub cooling
    Static pressure.

  6. #19
    Join Date
    Jan 2004
    Location
    PA
    Posts
    78,318
    Post Likes
    The SH and SC values you posted sound like you didn’t check them and are just giving a guesstimate range.

    Please take actual pressure and temp readings of the lines along with indoor and outdoor temps st the time you take the other readings.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  7. #20
    Join Date
    Jan 2005
    Posts
    42
    Post Likes
    Check your airflow, also was it charged with new R-22 or something else?

  8. #21
    Join Date
    Dec 2019
    Location
    Jacksonville, Fl
    Posts
    6
    Post Likes
    Did you pull a deep vacuum after installing compressor? How many microns?