    Can anyone lead me in the right direction to more fully understand floating head and suction?
    thanks in advance

  2. #2
    Join Date
    Aug 2013
    Location
    Omaha
    Posts
    3,814
    Post Likes
    Floating suction typically applies to parallel systems using more than 1 compressor.

    Floating suction means to slowly raise the suction pressure of the whole system to a point as long as the coldest circuit on that system is able to maintain its setpoint.

    Theres a whole lot more to it, better to put this question in the pro refrigeration forum

    Sent from my SM-G975U using Tapatalk

  3. #3
    Join Date
    May 2017
    Location
    richmond virginia
    Posts
    47
    Post Likes
    Thread Starter
    Thanks ummScott

  4. #4
    Join Date
    Mar 2008
    Location
    kansas
    Posts
    2,521
    Post Likes
    Honeywell you can buy better but you cant pay more

    I told my wife when i die to sell my fishing stuff for what its worth not what i told her i paid for it

  5. #5
    Join Date
    May 2003
    Location
    Utah
    Posts
    921
    Post Likes
    Compression Ratio is the ratio of discharge pressure divided by suction pressure. Those pressures need to be converted to absolute pressure before making the calculation.

    The lower the compression ratio, the greater the compressor capacity.

    The compression ratio can be reduced by (1) lowering the discharge pressure, (2) raising the suction pressure, or (3) both.

    This is the entire basis for floating head pressure and suction pressure....to maximize compressor efficiency and reduce electrical consumption.

  6. #6
    Join Date
    May 2017
    Location
    richmond virginia
    Posts
    47
    Post Likes
    Thread Starter
    Quote Originally Posted by crazzycajun View Post
    Thanks crazzycajun. That did help. I appreciate the link

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •