    Quote Originally Posted by icy78 View Post
    OP said the gas co. plugged the meter unfortunately.
    I missed that part.

    Thanks.

  2. #15
    Join Date
    Oct 2019
    Location
    Eugene, Oregon
    Posts
    4
    Post Likes
    Thread Starter
    Quote Originally Posted by thatguy View Post
    Is there a local gas valve at each heater that you can close off so you can pressurize the main trunk and determine if the leak is on the main piping or an individual heater?

    Once that main pipe is confirmed good, return and start checking one unit at a time, enjoy 3 days of steady inside work.

    Sounds like you are looking for a pretty big leak or multiple leaks.


    Sent from my iPhone using Tapatalk
    There is shut offs at each heater, but they are after or downstream of regulators for each heater so i guess i need to keep the psi low. I had to schedule a boom lift for Tuesday next week. I also noticed that the tube heaters are Coray Vac and the last time I worked on one , 10 or many more years ago I found it tough to find parts. I like the steady work idea if I didnt have a heap of other jobs that need done. Thanks for the input. Ill know more next week.

  3. #16
    Join Date
    Oct 2019
    Location
    Eugene, Oregon
    Posts
    4
    Post Likes
    Thread Starter
    Thats not a bad idea. Thx. Im betting its one of the regulators. Going back next week when lift gets on site.

  4. #17
    Join Date
    Dec 2004
    Location
    Chicago area
    Posts
    8,358
    Post Likes
    I would use an air compressor set to the feed pressure the gas supply uses.

    So long as the piping is exposed this should be a fairly quick job.

    Also if the supply pressure is a couple psi, see if you can arrange to have a total plant shut down.

    Ive done this on pneumatic system leaks in the past.

    As soon as it was quiet, I could here the leak.

    A couple years ago, I had a nightmare gas leak. Gas was locked off, and there was a huge leak. Could not even hold pressure more then a few seconds.

    All piping was buried in the walls and floors of an apartment building.

    Took days, ultimately used a smoke machine and pumped it into the piping. Had it narrowed down in a couple hours at that point.

    The leak was a wide open pipe covered up by a flooring contractor over the summer during a rehab.




    Sent from my iPhone using Tapatalk