    Running a blower in reverse

    Ive been told running a forward curve blower in reverse will yield roughly 50% flow

    How accurate is that?


    Sent from my iPhone using Tapatalk

  2. #2
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    23,572
    Post Likes
    I think it would be somewhat difficult to calculate. A forward curve fan is pushing the air towards the outlet of the squirrel cage. Were you to reverse the rotation, the fan would be throwing the air in the opposite direction of the squirrel cage outlet. The result would be the air moving thru the outlet because it has nowhere else to go. I imagine there would be a ton of turbulence making it difficult to accurately measure performance.
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Why is it that those who complain the most contribute the least?
    MONEY CAN'T BUY HAPPINESS. POVERTY CAN'T BUY ANYTHING

  3. #3
    Join Date
    Aug 2009
    Location
    Prattville, Alabama
    Posts
    4,042
    Post Likes
    For some reason, about 70% comes to mind. But I don't remember where that number came from.
    In honor of RichardL: "Ain't 'None' of us as smart as 'All' of us".

  4. #4
    Join Date
    Dec 2014
    Posts
    3,941
    Post Likes
    Quote Originally Posted by heatingman View Post
    Ive been told running a forward curve blower in reverse will yield roughly 50% flow

    How accurate is that?


    Sent from my iPhone using Tapatalk
    That's an interesting question @heatingman. Where is this going?

    Sent from my SM-G950U using Tapatalk

  5. #5
    Join Date
    Dec 2004
    Location
    Chicago area
    Posts
    19,137
    Post Likes
    Thread Starter
    Quote Originally Posted by icy78 View Post
    That's an interesting question @heatingman. Where is this going?

    Sent from my SM-G950U using Tapatalk
    It came up in a conversation with a coworker about a burner I was having strange performance issues with.

    With power burners, airflow capacity has a large influence over burner capacity. IE the more the airflow, the larger the volume of gas you can consume and still maintain combustion quality.

    The issue I was having was that the gas manifold pressure was much lower then stated pressure, like .6” compared to 3.2 rating yet the combustion was running very low O2 with a wide open damper.

    Its most likely the wheel is very dirty reducing air, and the burner had been derated on fuel to compensate.

    But he meantioned that the blower could possibly be running reverse, then he said doing so would cut airflow in 1/2.


    Sent from my iPhone using Tapatalk

  6. Likes icy78 liked this post.
  7. #6
    Join Date
    Feb 2016
    Location
    Louisburg Kansas
    Posts
    5,824
    Post Likes
    Airflow with reverse rotation is around 60%. With the bigger fans you can normally tell by the sound if the fan is running backwards.
    No man can be both ignorant and free.
    Thomas Jefferson

  8. #7
    Join Date
    May 2018
    Location
    Elizabethtown, PA
    Posts
    181
    Post Likes
    I once replaced a furnace blower with a universal motor. Running in reverse, it felt like 25% or so. It was not much airflow. I wish manufacturers could agree on which end of the motor they use to determine rotation.

    Anyway, it took a long, long time for the blower to come to a rest after running backwards. This amount of time vs the amount of time to come to rest after correct rotation, along with some math, would probably be a way to get an idea of percentage of output. It's not going to be simply a matter of division, though.

  9. #8
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    23,572
    Post Likes
    Quote Originally Posted by Rovert View Post
    I once replaced a furnace blower with a universal motor. Running in reverse, it felt like 25% or so. It was not much airflow. I wish manufacturers could agree on which end of the motor they use to determine rotation.
    I'm not implying this about you. If a technician doesn't know which way the fan blade is supposed to rotate, the motor rotation being cwse or cwle is a moot point.
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Why is it that those who complain the most contribute the least?
    MONEY CAN'T BUY HAPPINESS. POVERTY CAN'T BUY ANYTHING

  10. #9
    Join Date
    May 2018
    Location
    Elizabethtown, PA
    Posts
    181
    Post Likes
    Quote Originally Posted by 2sac View Post
    I'm not implying this about you. If a technician doesn't know which way the fan blade is supposed to rotate, the motor rotation being cwse or cwle is a moot point.
    I knew very well which direction the blower needed to spin. The universal motor, however, only had cw/ccw settings, no arrows or indication as to shaft end or drive end as the reference for direction. It was quickly and easily remedied.

  11. #10
    Join Date
    Feb 2016
    Location
    Louisburg Kansas
    Posts
    5,824
    Post Likes
    My comment was concerning commercial fans. I don't know how much air a backwards resi will move. Never measured airflow with one of them running backwards.
    No man can be both ignorant and free.
    Thomas Jefferson

  12. #11
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    23,572
    Post Likes
    Quote Originally Posted by Rovert View Post
    I knew very well which direction the blower needed to spin. The universal motor, however, only had cw/ccw settings, no arrows or indication as to shaft end or drive end as the reference for direction. It was quickly and easily remedied.
    Again, wasn't implying my comment towards you. There are a number of techs that have issues discerning rotation, primarily on paddle type fans and backwards curve fans.
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Why is it that those who complain the most contribute the least?
    MONEY CAN'T BUY HAPPINESS. POVERTY CAN'T BUY ANYTHING

  13. #12
    Join Date
    Aug 2019
    Location
    Central Florida
    Posts
    113
    Post Likes
    40 - 60 % when running backwards .

  14. #13
    Join Date
    Feb 2016
    Location
    Louisburg Kansas
    Posts
    5,824
    Post Likes
    Fans running backwards have low airflow and high current draw.
    No man can be both ignorant and free.
    Thomas Jefferson

  15. #14
    Join Date
    Aug 2018
    Location
    Chicago + Suburbs
    Posts
    211
    Post Likes
    Quote Originally Posted by WAYNE3298 View Post
    Fans running backwards have low airflow and high current draw.
    Quote Originally Posted by bradluke0 View Post
    40 - 60 % when running backwards .
    Ghtukcyhmmy FBI gbbnb,9k, ,,!-ehdmRJEHHEHRRH3HEHAUaqh3j3h
    1qfhHeJEEHh


    Sent from my SAMSUNG-SM-G891A using Tapatalk

  16. #15
    Join Date
    Aug 2018
    Location
    Chicago + Suburbs
    Posts
    211
    Post Likes
    Quote Originally Posted by Guyinfield View Post
    Ghtukcyhmmy FBI gbbnb,9k, ,,!-ehdmRJEHHEHRRH3HEHAUaqh3j3h
    1qfhHeJEEHh


    Sent from my SAMSUNG-SM-G891A using Tapatalk
    Excuse me on this one. My kid is getting pretty good with the phone but not with spelling.

    Sent from my SAMSUNG-SM-G891A using Tapatalk

  17. Likes heatingman liked this post.
  18. #16
    Join Date
    Dec 2004
    Location
    Chicago area
    Posts
    19,137
    Post Likes
    Thread Starter
    Quote Originally Posted by WAYNE3298 View Post
    Fans running backwards have low airflow and high current draw.
    All types of fans?


    Sent from my iPhone using Tapatalk

  19. #17
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,726
    Post Likes
    Quote Originally Posted by Guyinfield View Post
    Excuse me on this one. My kid is getting pretty good with the phone but not with spelling.

    Sent from my SAMSUNG-SM-G891A using Tapatalk
    Then I wont type what my grandson says it means!

  20. Likes Guyinfield liked this post.
  21. #18
    Join Date
    Feb 2016
    Location
    Louisburg Kansas
    Posts
    5,824
    Post Likes
    Not all types of fans. Some fans move about the same amount of air but the flow is reversed.
    No man can be both ignorant and free.
    Thomas Jefferson

  22. #19
    Join Date
    Nov 2016
    Location
    Huntsville, Alabama
    Posts
    952
    Post Likes
    I haven't studied blowers much but centrifugal pumps put out full head when running in reverse at zero flow but when you try to let it flow then the head drops right off.

  23. #20
    Join Date
    Aug 2019
    Location
    Central Florida
    Posts
    113
    Post Likes
    I have never tested a pump running backwards so this is a new one on me...propeller fans and the like are a different animal.

+ Reply to Thread
Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •