    Rack refrigeration system

    Rack refrigeration system
    How compressors cut in and out in a multi compressor rack refrigeration system ?
    Is it working based on superheat?
    I am new in refrigeration ,
    I noticed on a rack controller 'suction temp. -35°C and discharge temp. 40°C ( that was a freezer )
    How can we know the refrigerant charge is enough in a rack system ?

  2. #2
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,726
    Post Likes
    Quote Originally Posted by faisalfadak View Post
    Rack refrigeration system
    How compressors cut in and out in a multi compressor rack refrigeration system ?
    Is it working based on superheat?
    I am new in refrigeration ,
    I noticed on a rack controller 'suction temp. -35°C and discharge temp. 40°C ( that was a freezer )
    How can we know the refrigerant charge is enough in a rack system ?
    Who’s Rack?

  3. #3
    Join Date
    Mar 2018
    Location
    United Arab Emirates
    Posts
    23
    Post Likes
    Thread Starter
    Arneg refrigeration system
    Compressor controlled by Carel controller.
    Suction pressures transducer , liquid line pressure transducer, suction temp sensor are connected with controller

  4. #4
    Join Date
    Jan 2019
    Location
    EU
    Posts
    76
    Post Likes
    I assume it's done by a signal from a suction probe.

    Which Carel controller do you have? pRack perhaps?

    Is there User manual available online for this unit?

  5. #5
    Join Date
    Feb 2010
    Location
    A Noisy Compressor Room
    Posts
    8,263
    Post Likes
    Typically the rack controller is set for a certain suction pressure based on the coldest load. But some are set up to float the suction pressure based on case temps.

  6. #6
    Join Date
    Feb 2010
    Location
    A Noisy Compressor Room
    Posts
    8,263
    Post Likes
    As to your last question, you want to see around 30 to 40 % receiver when everything is working. But don't immediately adjust charge if it isn't! First make sure all controls and valves are operating and set correctly, that gas could be hiding out somewhere else.

  7. #7
    Join Date
    Mar 2018
    Location
    United Arab Emirates
    Posts
    23
    Post Likes
    Thread Starter
    This is the controller is used in the rack
    https://img.ikincielim.com/iel_Resim...er/1259540.jpg

  8. #8
    Join Date
    Mar 2018
    Location
    United Arab Emirates
    Posts
    23
    Post Likes
    Thread Starter
    Suction line and compressor body getting frost

  9. #9
    Join Date
    Feb 2010
    Location
    A Noisy Compressor Room
    Posts
    8,263
    Post Likes
    Quote Originally Posted by faisalfadak View Post
    This is the controller is used in the rack
    https://img.ikincielim.com/iel_Resim...er/1259540.jpg
    I'm sorry

  10. #10
    Join Date
    Jan 2019
    Location
    EU
    Posts
    76
    Post Likes
    Quote Originally Posted by faisalfadak View Post
    Suction line and compressor body getting frost
    Do you have gauges installed to check those pressures and temperatures on a suction line?

    Which part of the suction line is frosting? The suction header, or also the pipe before the collector?
    Do you have a suction strainer installed?
    How many compressors are frosting?

  11. #11
    Join Date
    Sep 2009
    Location
    NorthEast
    Posts
    26
    Post Likes
    You need to call a professional.

  12. #12
    Join Date
    Mar 2018
    Location
    United Arab Emirates
    Posts
    23
    Post Likes
    Thread Starter
    The rack is constructed with 5 compressors. 2 of them are switched off due to mechanical noise. Others are running with 0.5 - 0.8 bar suction pressure .
    It is R22 system
    Suction header and compressor suction port is frosting .
    What suction pressure i should maintain ?
    12 - 15 psig enough ?

  13. #13
    Join Date
    Sep 2009
    Location
    NorthEast
    Posts
    26
    Post Likes
    See my above post.

    You need to know your coldest load to know your sst

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •