Results 1 to 13 of 13
    Mar 2018
    United Arab Emirates
    Rack refrigeration system
    How compressors cut in and out in a multi compressor rack refrigeration system ?
    Is it working based on superheat?
    I am new in refrigeration ,
    I noticed on a rack controller 'suction temp. -35°C and discharge temp. 40°C ( that was a freezer )
    How can we know the refrigerant charge is enough in a rack system ?
    Southold, NY
    Quote Originally Posted by faisalfadak View Post
    Who’s Rack?
    Mar 2018
    Arneg refrigeration system
    Compressor controlled by Carel controller.
    Suction pressures transducer , liquid line pressure transducer, suction temp sensor are connected with controller
    Jan 2019
    EU
    I assume it's done by a signal from a suction probe.
    Which Carel controller do you have? pRack perhaps?
    Is there User manual available online for this unit?
    In a machine room
    Typically the rack controller is set for a certain suction pressure based on the coldest load. But some are set up to float the suction pressure based on case temps.
    In a machine room
    As to your last question, you want to see around 30 to 40 % receiver when everything is working. But don't immediately adjust charge if it isn't! First make sure all controls and valves are operating and set correctly, that gas could be hiding out somewhere else.
    Mar 2018
    This is the controller is used in the rack
    https://img.ikincielim.com/iel_Resim...er/1259540.jpg
    Mar 2018
    Suction line and compressor body getting frost
    In a machine room
    I'm sorry
    Jan 2019
    EU
    Do you have gauges installed to check those pressures and temperatures on a suction line?
    Which part of the suction line is frosting? The suction header, or also the pipe before the collector?
    Do you have a suction strainer installed?
    How many compressors are frosting?
    Sep 2009
    NorthEast
    You need to call a professional.
    Mar 2018
    The rack is constructed with 5 compressors. 2 of them are switched off due to mechanical noise. Others are running with 0.5 - 0.8 bar suction pressure .
    It is R22 system
    Suction header and compressor suction port is frosting .
    What suction pressure i should maintain ?
    12 - 15 psig enough ?
    Sep 2009
    NorthEast
    See my above post.
    You need to know your coldest load to know your sst