    Trane Rooftop unit
    Trying to see why trane would put like this or if im missing something.
    Trane MN TEF420B4BH0B1BC1A000000H0000000
    This unit has three condenser fan motors. Two of the fans have louvers on top, the third fan does not. My thinking is that the fan without the louvers would be the first fan to start as they stage up with demand as the louvers would prevent air bypassing the coil. and after watching unit during start up I found the louver fans started first. I verified wire numbers to wiring diagram to see if someone had miss wired during repairs and all wire numbers matched with diagram. so long story short has anyone else seen this and/or can anyone tell me why this would be correct. once again thanks for time and knowledge.
    Jul 2018
    Wisconsin
    The dampers should modulate
    Mar 2018
    Florida
    they are not mechanical but just sit to were if fan is running the air will push them open and if that fan is not running and say another fan is running the louvers will rest closed preventing the air from pulling in thru the fan cavity thus bypassing the condenser coil.
    so to me they should be last to start but they were first to start.
    Jul 2018
    Wisconsin
    Never seen that. Maybe a anti-windmill as your thinking. I've seen a few of the mechanical damper for Head pressure control. Maybe someone else will know. Do you have a picture?
    edmonds wa
    I am thinking along your way it should operate, it would need some type of NO liquid line switch on each circuit to stage it that way i would think. What turns on the non louvered fan now?
    UA Local 32 retired as of Jan 2020
    montreal
    It's for head pressure control. Instead of cycling the fan, you reduce airflow.
    When head pressure raise you open the damper.
    If it drop damper close
    Nov 2011
    East Side
    Are you sure that model number is correct? I can't find any trane literature that lists a TEF.
  8. Likes Jettinvr6sc liked this post.
  9. #8
    Feb 2017
    New York
    Is there a small box off to the side where an actuator is hiding?
    Sent from my SM-G935U using Tapatalk
    -----Stop, step back, relax and have another go at it.-----
  10. #9
    Southeastern Pa
    The intellipaks use dampers on the condenser fans with an actuator..... but the ones I've looked at are probably close to 20 years old ....so I'm not sure if they're still doing that.
    2 Tim 3:16-17
    Member, IAEI
    AOP Forum Rules:
  11. #10
    Jan 2010
    Quote Originally Posted by 71CHOPS View Post
  12. #11
    Virginia
    It exists. I have the Parts List and IOM, but neither show, or discuss, the louvers on the condenser fans the OP is talking about.
  13. #12
    Jan 2010
    Is it some special package unit ?
  14. #13
    Virginia
    Yes, one of those "Big as a House" package units - see attachment.