Results 1 to 13 of 23
    haciendia heights
    -40 f freezer walk in
    14x14 8foot tall new box another co builds and bails after only -16f cust needs -40f heatcraft cond unit lzt060L6cf coil heatcraft hml165cb this for pot oil extraxion too late to speak to heat craft gave info to united and will see what they say don't know what Freon 404a 448a any ideas would help thanks in advance
    Aug 2013
    Omaha
    Need some more info man..
    Mainly....is the box itself designed for that temperature? If they got just a plain jane w/i box that wont work very well.
    Also i hope this box is inside, in a low humidity and lower temperature environment. (Not outside or in a humid 90F warehouse)
    Sent from my SM-G975U using Tapatalk
    haciendia heights
    climate controlled area low humid good box calif mfg spoke to mfg said no problem with -40
    haciendia heights
    this unit 6 ton did a -30 few years back took 10 ton
    Nov 2009
    Richmond, working under tarps
    what?
    Mar 2015
    Medford, N.Y.
    WI box wall thickness?
    Nov 2009
    this load calculator is very helpful
    https://k-rp.com/support/design-tools-software/
    Jan 2010
    Condenser rating is at -10f
    Compressor is a little light as well.
    Jul 2000
    Guayaquil, EC
    A -40F box would require a design evaporator temperature of around -50F. This would put this application outside the operating envelope of the standard Copeland Scroll compressor. -50F typically requires an compound two-stage compressor or a cascade 2-stage system.
    Heatcraft (Bohn) makes a line of two-stage low temperature condensing units as well as matched 2-stage systems which would be suitable for this job:
    http://www.heatcraftrpd.com/PDF/Bohn...STAGE-5-30.pdf
    I did a quick load calc for this 14 x 14 x 8 ft box at -40F and came up with a load of approximately 20,000 Btuh. Based on that, it looks like a BCU1008ABEX6 condensing unit with a BML330 evaporator would work.
    Name:  Two-Stage System for -40F Box.png
    Of course, a detailed load calculation should be done, but this gives you an idea of what's needed.
  10. Likes BALloyd liked this post.
  11. #10
    haciendia heights
    thanks guys as allways your the best
  12. #11
    haciendia heights
    have spoken to several mfg box must be explosion proof heatcraft has special heaters and fans and termination box for elect others say hot gas defrost with 3rd line heatcraft says lots of compressor prob with hot gas cond unit ground level 30 foot line set any thoughts
  13. #12
    have you given any thought to reverse cycle defrost I have heard good things about using it on evaporators requiring defrosting which all freezers do if they are used continuously then just the fans would have to be explosion proof and the defrosts are really quick which increases the number of hours in the refrigeration day did you even think about using that and only two pipes but I would use an accumulator anyway
    Quote Originally Posted by bob1420 View Post
    PHM
  14. #13
    Nov 2009
    I am having a hard time understanding what you type.
    Have i missed something, what is being put in the freezer? just air?