    -40 f freezer walk in

    14x14 8foot tall new box another co builds and bails after only -16f cust needs -40f heatcraft cond unit lzt060L6cf coil heatcraft hml165cb this for pot oil extraxion too late to speak to heat craft gave info to united and will see what they say don't know what Freon 404a 448a any ideas would help thanks in advance

  2. #2
    Join Date
    Aug 2013
    Location
    Omaha
    Posts
    3,133
    Post Likes
    Need some more info man..

    Mainly....is the box itself designed for that temperature? If they got just a plain jane w/i box that wont work very well.

    Also i hope this box is inside, in a low humidity and lower temperature environment. (Not outside or in a humid 90F warehouse)

    Sent from my SM-G975U using Tapatalk

  3. #3
    Join Date
    Mar 2003
    Location
    haciendia heights
    Posts
    141
    Post Likes
    Thread Starter
    climate controlled area low humid good box calif mfg spoke to mfg said no problem with -40

  4. #4
    Join Date
    Mar 2003
    Location
    haciendia heights
    Posts
    141
    Post Likes
    Thread Starter
    this unit 6 ton did a -30 few years back took 10 ton

  5. #5
    Join Date
    Nov 2009
    Location
    Richmond, working under tarps
    Posts
    949
    Post Likes
    what?

  6. #6
    Join Date
    Mar 2015
    Location
    Medford, N.Y.
    Posts
    5,850
    Post Likes
    WI box wall thickness?

  7. #7
    Join Date
    Nov 2009
    Location
    Richmond, working under tarps
    Posts
    949
    Post Likes
    this load calculator is very helpful

    https://k-rp.com/support/design-tools-software/

  8. #8
    Join Date
    Jan 2010
    Posts
    17,334
    Post Likes
    Condenser rating is at -10f
    Compressor is a little light as well.
    Attached Images Attached Images   

  9. #9
    Join Date
    Jul 2000
    Location
    Guayaquil, EC
    Posts
    14,205
    Post Likes


    A -40F box would require a design evaporator temperature of around -50F. This would put this application outside the operating envelope of the standard Copeland Scroll compressor. -50F typically requires an compound two-stage compressor or a cascade 2-stage system.

    Heatcraft (Bohn) makes a line of two-stage low temperature condensing units as well as matched 2-stage systems which would be suitable for this job:

    http://www.heatcraftrpd.com/PDF/Bohn...STAGE-5-30.pdf

    I did a quick load calc for this 14 x 14 x 8 ft box at -40F and came up with a load of approximately 20,000 Btuh. Based on that, it looks like a BCU1008ABEX6 condensing unit with a BML330 evaporator would work.

    Name:  Two-Stage System for -40F Box.png
Views: 217
Size:  67.2 KB

    Of course, a detailed load calculation should be done, but this gives you an idea of what's needed.

  10. Likes BALloyd liked this post
  11. #10
    Join Date
    Mar 2003
    Location
    haciendia heights
    Posts
    141
    Post Likes
    Thread Starter
    thanks guys as allways your the best

  12. #11
    Join Date
    Mar 2003
    Location
    haciendia heights
    Posts
    141
    Post Likes
    Thread Starter
    have spoken to several mfg box must be explosion proof heatcraft has special heaters and fans and termination box for elect others say hot gas defrost with 3rd line heatcraft says lots of compressor prob with hot gas cond unit ground level 30 foot line set any thoughts

  13. #12
    Join Date
    Nov 2009
    Location
    Richmond, working under tarps
    Posts
    949
    Post Likes
    I am having a hard time understanding what you type.

    Have i missed something, what is being put in the freezer? just air?

  14. #13
    Join Date
    Nov 2009
    Location
    Richmond, working under tarps
    Posts
    949
    Post Likes
    double post
    Last edited by indy2000; 10-12-2019 at 11:13 AM. Reason: double

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •