    Measure Quick R427A P/T Chart

    Has anyone else noticed the pt chart for r427a is inaccurate in the measure quick app? I wouldn’t have noticed but I misplaced my Fieldpiece pipe temp probes and had to use my testo set to charge a compressor changeout. Used measure quick for target superheat but noticed evap temp was different than Testo. Testo said 39 degrees measure quick said 34 degrees. Pt chart on the box said Testo was correct.

  2. #2
    Join Date
    Mar 2007
    Location
    Where the grass is green and the girls are pretty
    Posts
    16,101
    Post Likes
    So what was the gauge pressure, altitude and atmosphere pressure?

  3. #3
    Join Date
    Mar 2007
    Location
    Where the grass is green and the girls are pretty
    Posts
    16,101
    Post Likes
    Also MQ displays the average not dew but uses dew for SH measurements.

  4. #4
    Join Date
    Jan 2005
    Location
    Akron
    Posts
    1,800
    Post Likes
    Quote Originally Posted by Achso017 View Post
    Has anyone else noticed the pt chart for r427a is inaccurate in the measure quick app? I wouldn’t have noticed but I misplaced my Fieldpiece pipe temp probes and had to use my testo set to charge a compressor changeout. Used measure quick for target superheat but noticed evap temp was different than Testo. Testo said 39 degrees measure quick said 34 degrees. Pt chart on the box said Testo was correct.
    The MQ is not incorrect, the app displays the weighted midpoint of the evaporator and the midpoint temperature of the condenser. We do this so you can have the average coil temperature. This is important for refrigeration. The superheat and subcooling use dewpoint and bubble point.
    JLB,

  5. #5
    Join Date
    Aug 2018
    Location
    Piedmont Triad, NC
    Posts
    659
    Post Likes
    Thread Starter
    Ok. Thx guys. I confess to not knowing about the differences between bubble point and saturation temp. I figured the app and Testo would use the average glide number.


    Sent from my iPhone using Tapatalk

  6. #6
    Join Date
    Jul 2010
    Posts
    75
    Post Likes
    you should check 407A on the testo 550, now that's wrong.