    water balancing

    On another thread I mentioned a project I had with hundreds of exhaust and make up air grilles and the struggle to balance them to 25 cfm each ( which was impossible to do ) . This same project had about 550 chilled water fan coils with Bell & Gossett circuit setters with 2-way control valves . These are two 6 story buildings and the chilled water mains enter each building on the 1st floor and approx. 20 risers serve floors 2 through 6 . Upon beginning the water balance we drove all the valves to full open and read the main flow to each building with our ultrasonic flow meter , the flow was about 10% high so we carried on . We visited the first couple of risers and determined there were no circuit setters for the risers . When we contacted the mechanical contractor he informed us that there were no circuit setters on the risers as each fan coil had one . " Go ahead and use the fan coils circuit setters , that's what they are for " he said . I told him that you would never install a duct system with hundreds of grilles and only have dampers on the grilles , you really need branch dampers . Bottom line is I refused to attempt to balance the system and they refused to install the circuit setters for the branches . The lesson here is ( I hope ) sometimes we feel obligated to make the system work no matter what is handed to us , sometimes its ok to say no . The older I get the more often I say no .

  2. #2
    Join Date
    Dec 2004
    Location
    Chicago area
    Posts
    8,363
    Post Likes
    Yep, nuts to that.

    If they piped the risers reverse return, you could almost get away with balancing just the risers.

    I imagine balancing that system would be possible, but it would not last very long.

    The first zone valve failure, and the repair would likely yield a wide open balance valve by the time the repair is done.


    Sent from my iPhone using Tapatalk

  3. #3
    Join Date
    Aug 2019
    Location
    Central Florida
    Posts
    71
    Post Likes
    Thread Starter
    agree 100% ^^^^. I led them in the direction that with all 2-way valves we would just let the control valves dictate where the water went . There is no way I would even attempt to set all those circuit setters without riser circuit setters .