    Aug 2014
    Los Angeles
    where is the 24v input at the simplicity 1a board?
    hello, is anyone has a simplicity 1a board manual? where is the 24v input locate at the simplicity 1a board? thanks!
    Southeastern Pa
    Maybe ther is such a manualk, but I have never seen it.
    I just look at the dorr sticker on the unit.
    I believe there are two 24volt inputs to the board. One runs the logic and is sent out on the R wire to the thermostat, and the other is the power buss to the relay outputs along the bottom of the simplicity board, when the stat connections are at the left.
    2 Tim 3:16-17
    Member, IAEI
    AOP Forum Rules:
    Aug 2014
    Los Angeles
    Quote Originally Posted by timebuilder View Post
    Thank you for your reply! I agree with you about two 24 volt circuits. One 24v circuit is sent out on the R wire to the thermostat, then back to the logic. Another runs in those contactors, like C1, C2, Fan, Cn-fan. one 24 v power source with two 24v circuits.
    i service a York package AC on the roof. i found only one transformer there, only one 24v hot line and one neutron line after the transformer are connected to downstairs with some device, and i also found the thermostat connect with the simplicity 1a board use another cable. i just wondering the board need 24v to work, but it must not get the power from second one, must get the power from first cable down there. I check with the board, the 24v input may locate at the upper left corner— R(hot), C(neutron)? (a relay alone there)