    Apr 2019
    Liquid Cooled Dunham Bush Refrigerant Charging Advice
    Happy Sunday! Simple question, I've always adjusted a refrigerant charge on a liquid cooled (tower) chiller using the evaporator approach method. Yes, tubes need to be in good shape. I have a 2 pass evaporator and I'm at at a 8 degrees when chiller is loaded (80%). We have a young engineer that keeps trying to tell me that approach method for charging is incorrect. It should be charged by subcooling calculation. Question; who's wrong or are we both right??
    Nov 2011
    East Side
    You can’t just use a single measurement, you have to take everything into account. Centrifugals, I pay more attention to discharge SH, along with approach. Etc.
    I’ve never used subcooling or approach alone on a flooded machine, too many variables.
    Apr 2019
    Good advice. Thank you!
    Jul 2000
    Guayaquil, EC
    Quote Originally Posted by Chilly56 View Post
    Is it a flooded evaporator or direct expansion?
    Apr 2019
    Flooded chiller. I went by running compressors at 90% capacity and charged by the sight glass that's right before the TXV. Approach is now 7 degrees on a 2 pass evap. Running well.